Ready for the next layer of complexity? So far we have assumed we have a single installation with no bonding.

Add in some parallel paths from bonding of any extraneous parts, these all effectively act as earth rods.

Then consider that there may be more than one installation on the downstream side of the fault, so there you have more than one earth electrode in parallel.

And the DNO side of things will have various earth rods along the length of the distributing main.
Gosh Dave. Too many variables there for me to plug into a neat equation 😳
 
I love the maths. I just wish my physics was even half as good.

I did get a bit carried away! I've got yet another cracked rib from battling with the youngsters (trying jiu jitsu now), so am at a loose end.

It's @davesparks fault for edging me forward with more and more complicated scenarios 😄
Yeah I’m the same I just believe in the total immersion theory….I just keep reading and trying even though I’m out of my depth and slowly but surely things make sense 😂…..
 
Haha... we do go around in circles on this forum don't we. Oh well, a little something new comes up with each similar thread.
I just love that there are clever people around who are willing to help.
Add in some parallel paths from bonding of any extraneous parts, these all effectively act as earth rods.
A TT house I was looking at yesterday was giving a Zs of 0.43 ohms at a socket.
It turned out to be via copper gas pipes and the PME supply next door (there was external meter box, they were out, so I had a sneaky look!)
Yes a single additional earth rod may be quite useless, but if every installation connected to a PME distributing main has an additional earth electrode it could make a difference.
I agree, but I'd like to see it rolled out in a more coordinated and considered way. Depending on where a supplier N breaks, and where the DNO's own electrodes are you could end up with several properties diverted neutral current going via the one house where an enlightened sparks fitted the extra rod.
 
I agree, but I'd like to see it rolled out in a more coordinated and considered way. Depending on where a supplier N breaks, and where the DNO's own electrodes are you could end up with several properties diverted neutral current going via the one house where an enlightened sparks fitted the extra rod.

Is there a more coordinated way to roll it out?

Unfortunately it has to start somewhere and yes such situations will occur but in the fullness of time they will sort themselves sout
 
As folks have pointed out many time, a single rod will make little difference but if you have a dozen or two homes on a faulted segment then all those rods is getting down to a decent Ra. Also they are probably achieving some vague semblance of balance on the 3-phase you might only have low tens of amps imbalance to deal with and not the total of hundred-ish or so that simply adding the typical house values up gives.

The USA has had this for a while but not a very good specification (two rods of given size, no spec on Ra) and the ROI has been doing this with TN-C-S

It is a shame that AM2 did not go with the requirement for new properties to have foundation rebar bonded, etc, as that would get decently low Ra in most cases.
 
Also they are probably achieving some vague semblance of balance on the 3-phase you might only have low tens of amps imbalance to deal with and not the total of hundred-ish or so that simply adding the typical house values up gives.
It's only just occurred to me that while this is a clear benefit, there is also technology relying on phase imbalance and arising volt drop/raise to detect the condition in the first place, e.g. the indent 4 EV chargers and Matt-e devices who look for <207 or >253V. In theory could the phase balance improve to a degree that these devices wouldn't function?

I actually feel it should be the DNO's responsibility to deliver an acceptable supply with an acceptable number of real earth connections rather than pushing the onus onto the customers to add electrodes to support the network.
If it get's 'fixed' at the point of the customer installation then that precludes any future technological advances for detecting the conditions, e.g. micro-controller based monitoring typical voltage ranges, maybe even smart connected and monitored, or going back to a form of the VOELCB technology to detect a PEN-real Earth potential difference.

I accept that once a critical mass is reached this will make touch-voltages a lot safer, but my fear is that it will hide the problem better as well.
 
It's only just occurred to me that while this is a clear benefit, there is also technology relying on phase imbalance and arising volt drop/raise to detect the condition in the first place, e.g. the indent 4 EV chargers and Matt-e devices who look for <207 or >253V. In theory could the phase balance improve to a degree that these devices wouldn't function?
Indeed
This is precisely why version 2 of the Zappi charge point also has a separate CT to monitor the earth cable as well as built in OPen protection.
 
It's only just occurred to me that while this is a clear benefit, there is also technology relying on phase imbalance and arising volt drop/raise to detect the condition in the first place, e.g. the indent 4 EV chargers and Matt-e devices who look for <207 or >253V. In theory could the phase balance improve to a degree that these devices wouldn't function?

The devices will function as their purpose is to prevent danger arising from an open PEN fault. If other protective measures have already reduced the danger to a level where these devices don't detect it or operate then they aren't needed to operate at that point.
 
I’ve just mentioned those John ward videos on another thread. he is brilliant.

the only problem I have with this particular video is he explains how to do it then explains how it may not work. leaving me more confused and out of my depth that I was before.

However his explanations are brilliant and easy to follow and understand, but designing new circuits and deciding on the earthing systems is becoming a nightmare.
 