Gosh Dave. Too many variables there for me to plug into a neat equationReady for the next layer of complexity? So far we have assumed we have a single installation with no bonding.
Add in some parallel paths from bonding of any extraneous parts, these all effectively act as earth rods.
Then consider that there may be more than one installation on the downstream side of the fault, so there you have more than one earth electrode in parallel.
And the DNO side of things will have various earth rods along the length of the distributing main.

…..