HI all. I am not an electrician and know only but a few things about it so I want to ask a question .
So Chargemaster is supposed to install a home charging unit on my property. Their technician came and said I needed additional electrical work (either an double pole isolation switch or run a 6mm cable from my board next to the main distribution and change a breaker from 16 to 32. I went for the 2nd option as it was cheaper.
The other thing he asked was to call my DNO to lower my earthing as my Ze was 0.44 on a TCNS system and they need it 0.35 and lower.
UK Power Networks does not offer appointments and they deal as if and when they are available on last minute notice so it can take forever.
When the electrician came to run the cable I asked him to measure the Ze and he found it at 0.24

1) Can the Ze change from day to day or time to time or did someone get it wrong (I think the Chargemaster one because he didnt very keen to work that day)
2) Could the whole Ze thing be bypassed if they install an earthing rod with the charging unit (I know Chargemaster does that but their technician did not even mention it)

Thank you all for the help in advance
 
Hi - the values for Ze you have posted would not have stopped me proceeding as they are both ok, in my humble opinion. For what it’s worth I noticed the Ze at my house dropped a similar amount last year, no doubt due to improvement works by DNO upstream from me.

If a rod is used as the means of earthing for an installation then the earth fault disconnect is managed by your RCD and rod. So the installation becomes independent of the DNO for final circuit fault management.
 
Hi - the values for Ze you have posted would not have stopped me proceeding as they are both ok, in my humble opinion. For what it’s worth I noticed the Ze at my house dropped a similar amount last year, no doubt due to improvement works by DNO upstream from me.

If a rod is used as the means of earthing for an installation then the earth fault disconnect is managed by your RCD and rod. So the installation becomes independent of the DNO for final circuit fault management.
Sorry so I can understand it. If they install an earthing rod on their charging unit then it doesnt matter what the DNO Ze number is?
 
The short answer - for your purpose - yes.
Ze is the impedance looking back into the supply from Line (230V say) to E. If a rod is installed and utilised to provide the E then you can be independent of their E at your installation. However, there are safety concerns about 2 earthing systems in proximity (TNCS house and TT charge point) and a risk assessment is required to be done and satisfied. This may be why they didn’t mention the TT rod option to you perhaps(?).
 

Reply to Earthing Rods for EV Homecharging in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello All I was pondering an idea recently regarding the ground connection to my property. At present it has a combined Neutral to earth at the...
Replies
8
Views
1K
Hi all, Merry Christmas to everyone, and apologies for talking work during the holidays😅 I have my first EV charger install job early in the New...
Replies
14
Views
2K
Help please! I need a Tesla Gen 2 EV charger fitted in my garage which is 22m from the consumer unit. My electrician is proposing to route a 6mm...
Replies
15
Views
2K
Hi Guys, hopefully someone will know the answer. Testing an install on a (domestic) PME system I have a garage consumer unit supplied from one of...
Replies
17
Views
2K
Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
Replies
19
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock