Gents.
I did some earth loop tests on Rolec power pedestals (2x 16 amp outlets) that are harbour side, looped in and out from one another.
Three months ago I got Zs readings from about 1.2 ohms to 0.50 ohms. This time round the readings are all less than 0.01 ohm.
Megger MFT meter.
The RCD in each meter trips off just fine.
I am using a LO 3 wire test as I am plugging into the sockets (as usual) cannot take readings directly from terminals as there are over 300 to do.
What would cause such a drop in values, we are nowhere near a substation etc, anyway I would have seen low readings before if this was the case.
Any ideas ?
Many thanks.
Can you try a Zs test somewhere known (e.g. you own home) to see if it is sane? My suspicion is the MFT is faulty in some way.
Are they the Megger test leads? My own DiLOG seems to be calibrated for its own probes, though that could not account for as much as 0.5 ohm as I think they measure less anyway.
As low as 0.01 really would only be possible at a substation, and not a small one either!
Megger just calibrated and I have been doing the tests for a few days now, it is just these few that are odd.
The "old way" might be worth a try. Isolate and lock off circuit. Short R1+R2 at the socket. Then 2 wire high current test at the CU between bus bar and outgoing live. It's effectively extending the CPC back to the CU using R1.
Megger's have separate calibration settings for low current and high current. Low current tests can of course vary wildly in accuracy but 0.01 ohms is just daft.
sure you nit got tester on the 500V IR setting? 🤣🤣
Many thanks for the input, as it was ----ing down today I will have to check this out tomorrow.
Reply to Zs Readings seem to be a bit low. in the UK Electrical Forum area at ElectriciansForums.net
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Electrical2Go - Megger MFT Deals! Upgrade your toolkit with our exclusive offer! Purchase any of the Megger advanced multifunction testers –...
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Hi Guys. When measuring zs I get very high reading. Ze is 0.3 (tns), zdb is 0.21. r1 and rn are is 0.42. r2 is 0.72 , r1+ r2 is 0.29 . when I...
7K