Hi guys passed my 2391 six months ago and have been inspecting friends and family for free to gain experiance. Got my first paying job, got to fuse board and noticed no earth wires for lighting circuits, checked out a couple of light fittings and same here. how do I go about testing these circuits, eg R1+R2?. What code do I give them etc. Many thanks guys.
 
just list tht they dont comply with current regs and note that all class 1 lighting equipment should be changed to class 2, ie change metal fittings to plastic. or rewire lighting?

regarding coding for a pir or eicr there could be cause for arguement, personally i would code it as a 1 however as i would say there is an immediate cause of danger if metal fittings are present within the lighting circuit.
i would code it as a 2 if there were no metal fittings present and say it requires further attention. others will more than likely disagree.

as regards to the testing you will not beable to record values such as r2 or r1+r2 and should note why on the cert. you should however fill in all other results as normal.
 
Last edited by a moderator:
Try the ESC best practice guides they are quite a help if you have limited experience.
 
Code 4 - there is no requirement to update a lighting circuit without a CPC. It would however be sensible to note specific metal features (if present on said lighting circuit) for "improvement" ie code 2
 
Is the circuit RCD protected?
The ESC best practice guide suggests using Class ii fittings and accessories, protecting the circuit with an RCD and placing a warning lable to the effect that there is no CPC on the lighting circuits.
Such would be a Departure, but would (acording to the ESC) offer the same degree of safety as would be achieved if there was a CPC.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
No earth wires
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
7

Thread Tags

Advert

Thread statistics

Created
pburley,
Last reply from
Deleted member 26818,
Replies
7
Views
2,011

Advert