I'm running a 30 metre length of three core 16mm armour to feed a garage conversion which could have a high loading.
The cable will be run from the external meter box where I will split the meter tails via a Henley
The problem is There is naff all room in the box and I can't fit a switched fuse in there to protect the armour as the main cut out is 100A
Can I put the switched fuse of another suitable protection device at the other end to protect against overload?
Cheers
 
can yo not fit a switch fuse in a suitable IP65 adaptable box on the wall close to the meter box ?
 
I'm running a 30 metre length of three core 16mm armour to feed a garage conversion which could have a high loading.
The cable will be run from the external meter box where I will split the meter tails via a Henley
The problem is There is naff all room in the box and I can't fit a switched fuse in there to protect the armour as the main cut out is 100A
Can I put the switched fuse of another suitable protection device at the other end to protect against overload?
Cheers



It is possible to do it that way. There are requirements though.

Regards Chris
 
I dont think the DNO would be too happy with that arrangement, if they found out of course.:biggrin5:

There wouldn't be anything wrong with what you suggest, further in to an installation but, not at the origin IMO.
 
I dont think the DNO would be too happy with that arrangement, if they found out of course.:biggrin5:

There wouldn't be anything wrong with what you suggest, further in to an installation but, not at the origin IMO.

I see no reason for the DNO to have issues. The installation if designed correctly would meet the requirements of BS7671.

Regards Chris
 
At least you didn't ask THAT dreaded question........!!

And yes, you need to protect the cable so will have to find some form of additional box to house it in.
 
The way I see it, the first 30M of distribution cable would be relying on their service fuse for protection against short circuit, albeit with the added overload protection at the load end.


I'm not saying it's wrong or non compliant but, knowing the DNO as we do they are bound to come across it, see a cable directly connect to their service fuse with no additional protection visible, put 2 & 2 together, make 49 and throw the toys out of the pram.
 
Just a Thought,

He can put the switch fuse/Isolator within 3M of the origin, suitably labelled of course, I don't know if that will help the Op any, as I cannot see the installation
 
Last edited:
The way I see it, the first 30M of distribution cable would be relying on their service fuse for protection against short circuit, albeit with the added overload protection at the load end.

True Lenny, though everyone seems to be happy using the Dnos fuse for short circuit when using standard circuits, after all its the fuse which Annex Za uses to limit Let through and allows the consumer units to be rated higher, also the standard circuits where the Dno's fuse is providing back up protection, the i2t is used for determining CSA.

Do you have discrimination(short circuit) between a 32 amp type B MCB and a 100 amp 1361, what about larger MCB's, on a short the Dno's fuse is now providing short circuit protection to your circuits.



I'm not saying it's wrong or non compliant but, knowing the DNO as we do they are bound to come across it, see a cable directly connect to their service fuse with no additional protection visible, put 2 & 2 together, make 49 and throw the toys out of the pram.

Regards Chris
 
Just a Thought,

He can put the switch fuse/Isolator within 3M of the origin, I don't know if that will help the Op any, as I cannot see the installation

Absolutely but, the issue was the service head being in an external meter cabinet with no additional room for a switchfuse.

Mounting an additional enclosure adjacent to the meter cabinet has been suggested.
 
Well id suggest he utilizes 433.2.2 part (i).

Regards Chris


He could & I'm not disputing that, I mentioned it earlier. The only point I raised was regarding the DNO and their inability to se the wood for the trees. They want (or at least mine do) to see the additional protection within 3M of their service head, end of. They wont be told any different and I just wanted to make the OP aware of it.

BS 7671 isn't the be all & end all.
 
He could & I'm not disputing that, I mentioned it earlier. The only point I raised was regarding the DNO and their inability to se the wood for the trees. They want (or at least mine do) to see the additional protection within 3M of their service head, end of. They wont be told any different and I just wanted to make the OP aware of it.

BS 7671 isn't the be all & end all.

Well just remind them of this;

1 Definition Network ESQCR

Consumer’s installations in buildings are not intended to be included in the definition. Such installations should comply with the requirements of BS7671 Requirements for Electrical Installations or those of other relevant standards. Electrical distribution systems on offshore installations are also excluded from the definition, e.g. oil rigs.

So tell them to concentrate on there network and you will concentrate on your installation to the relevant standards.

As for there equipment in a premise then there is also this;

ESQCR

Equipment belonging to distributors and meter operators which is installed on consumers’ premises must be suitable for itspurpose and safe. Examples of such equipment include: cables, meters, distribution boards, isolators and switches.Such equipment must also be electrically protected by fuses, cut-outs or circuit breakers. For safety and technical reasons the protective device should be situated as close as reasonably practicable to the supply terminals. Where flats are supplied by rising mains, duty holders should ensure that all equipment upstream of the supply terminals at each flat benefit from adequate electrical and mechanical protection.
In order to demonstrate compliance with the requirements of regulation 24(1) duty holders should adopt the standards of construction and installation necessary to comply with BS7671 Requirements for Electrical Installations.

Regards Chris
 
Last edited:
Wouldn't that mean the only protection the 16mm would have is the 100A service fuse? I wouldn't even consider that as an option! I would also be doing everything I could to rcd protect the armoured.
 
I would also be doing everything I could to rcd protect the armoured.

I agree about protecting the submain, but you don't want an RCD at source (Why?) as it would/could trip the whole of the remote installation on an earth fault which is a good 30 M away !, no, RCD's local if required is far better IMO, besides if the RCD was at source would this not contravene the regs wrt circuit segregation ? (314.1).

Unless of course the Installation was TT, and then a time delayed 100mA may be required
 
Last edited:
why on earth would you want to RCD the SWA?
 
Can of worms lads?

Gazz I'm not wet behind the ears you know I know about the 100A and the 16mm , and why would I RCD a distribution circuit in Armour????
 
Wouldn't that mean the only protection the 16mm would have is the 100A service fuse? I wouldn't even consider that as an option! I would also be doing everything I could to rcd protect the armoured.

Gazzdid, please explain your RCD suggestion on the armoured cable....?
 
I would have thought the 100A service fuse protecting the 30M run was a big no-no. If someone puts a spade through the SWA, the supply for the whole house is lost until the DNO comes out? Daz.
PS I'm no expert, so feel free to pull this comment to bits :smiley2:
 
I would have thought the 100A service fuse protecting the 30M run was a big no-no. If someone puts a spade through the SWA, the supply for the whole house is lost until the DNO comes out? Daz.
PS I'm no expert, so feel free to pull this comment to bits :smiley2:

nothing wrong with your comment. a 60A sw fuse is the answer.
 
Hence why you protect the cable using an over-current device.
 
Yep fair enough. Just saw a couple of posts on page 1 that seemed to be saying you don't need the fuse - seemed strange. Daz
 
Yep fair enough. Just saw a couple of posts on page 1 that seemed to be saying you don't need the fuse - seemed strange. Daz

The question wasn't should we or should we not install it as obviously we should. We were debating on where it should go in relation to the service head.

Overcurrent protection doesn't necessarily have to be at the origin of a circuit, (433.2 refers) but when it comes to the DNO, they are a law unto themselves so in this instance it would be best IMO to place it at the origin.
 
Just trying to get this straight in my head so apologies!

If the overcurrent protection is at the end of the 30M run, the scenario of a spade through the SWA will not result in the fuse blowing, but will blow the service fuse.

I thought if the 60A switch-fuse was protecting the cable it should go at the origin?

Daz
 
We're talking two different types of protection here I.e overcurrent & short circuit.

Before we were mainly talking overcurrent protection which ad I said previously can be placed anywhere along the circuit, (433.2.2)

Reliance on the suppliers fuse for short circuit is debateable and IMO in this instance wouldn't be accepted by the DNO should they find out.

Sent from my BlackBerry 9800 using Tapatalk
 
Problem Solved

Got a 100mm x 190mm metal clad enclosure with 80A main switch and 63A MCB, its proteus(CEF) so not the best but it will do the job at origin, im going to have to move the mainswitch slightly in the meter cupboard to fit it in but at its the best i can do

cheers for the input, ive enjoyed reading it all!
 
View attachment 10506

And if he was he may have used the attachment as a guide

I never use that table, the one originally posted by Spin in the same ''STICKY THREAD'', is the one to use, and have done for a number of years now. In your link a 16mm SWA cable fails to meet compliance for a XLPE 3 core cable, whereas in the alternative table it DOES comply.... It would also comply in 2 core 16mm form as well!!


Table for 90[SUP]0[/SUP]C Thermosetting SWA cables operating at 70[SUP]0[/SUP]C.

Conductor CSA
Minimum CSA of SWA to meet 54G
CSA of armour 2 core
CSA of armour 3 core
CSA of armour 4 core
1.5
3.4
16
17
18
2.5
5.7
17
19
20
4
9.0
19
21
23
6
13.6
22
23
36
10
22.6
26
39
43
16
36.1
41
44
49
25
36.1
42
62
70
35
36.1
62
70
80
50
56.4
68
78
90
70
79.0
80
90
131
95
107.2
113
128
147
120
135.3
(125)
141
206
150
169.2
(138
201
230
185
208.6
(191)
220
255
240
270.6
(215)
(250)
289
300
338.3
(235)
(269)
(319)
400
451.0
(265)
(304)
(452)
 

Reply to Distribution circuit question in the Australia area at ElectriciansForums.net

Similar Threads

I'm doing a college design project and need to choose a suitable range of circuit protective devices for the whole contact. I've chosen and...
Replies
7
Views
4K
Hi, I have a book on domestic wiring which says that everywhere there is a change in current carrying capacity along a circuit there must be some...
Replies
3
Views
329
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
For context i am in my 2nd year in college and my head is going round in circles a question in my project for which i need to select the right...
Replies
22
Views
4K
Hi all. I have been asked to take over a job an electrician has started, and has moved abroad. The house is a big mansion, with a 3PH supply...
Replies
49
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock