  1. shower had incorrect isolation switch
  2. shower wired in 2.5mm cable
  3. shower suppl not on its own circuit
  4. earth not connected for circuit 3
  5. no earth sleeving circuit 4
  6. faulty switch on kitchen socket
  7. every circuit apart from the cooker had failed the insulation resistance test
thus the test conclusion was unsatisfactory.
guy then asked so all i need is to retest in 10 year :S
he was positive he doesnt need to rectify
property was rented out and he was landlord
yeah , i have done that and left comments on the sheets.
so ive done my part and fixed a C1 ( earth not connected)
just the fact he was thinking awell ill leave it and that having the report done was all he needed to do
well you would have been within your rights to issue a danger notice over that disconnected CPC in my eyes....
thats after of course his insistance that he do nowt about it....
regarding cpc i re connected as soon as i noticed .
basically this guys needs these circuits rewired that failed IR
flat is around 25-30 year old
but the fact that the shower is wired in 2.5mm through a sw/fuse spur from day 1 is SHOCKING , (theres no bath only shower)
heard from maintenance plumber that all the flats are F***** lol
Reply to just failed eicr in the UK Electrical Forum area at ElectriciansForums.net
Hi, recently had an EICR test done by 'Landlord Certificates' which failed due to circuite 3 having two radial circuits into a single 32amp MCB...
4K
Good day. First time poster. We recently had an electrician perform the EICR, as this is a newly purchased property I thought'd I would have the...
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Hi All Happy new year to all! First post but long timer lurker, so thanks for all the previous help! Just wanted to clarify something I have...
Went to fix a simple issue for someone . Then realised they where tenants and asked if they had a copy of the EICR ....NOPE . Turns out no Gas...