Hi guys I done a quick search but could not find a answer, earthing system in question is TN-S. Supply cable comes in is terminated into two 1361 cut outs and then one set tails then go through to next door into another 1361. Am I wrong in believing that in order to test ze properly the next door property should be isolated and removed from the MET to conduct the test?
 
You need to isolate the supply then remove all parallel earth paths, then you can carry out a Ze teat.
 
Hi guys I done a quick search but could not find a answer, earthing system in question is TN-S. Supply cable comes in is terminated into two 1361 cut outs and then one set tails then go through to next door into another 1361. Am I wrong in believing that in order to test ze properly the next door property should be isolated and removed from the MET to conduct the test?

Only the main earthing conductor to the second property needs to be isolated. So you will need to liaise with the neighbour before you disconnect the main earthing conductor to that property. Then proceed as normal to conduct the Ze test in the property you are working in...
There is no need to disconnect the line and neutral to the neighbours property.....
 
  • Like
Reactions: 1 person
Yh fully understand that otherwise the install would have no earth, as for the live conductors they are within sealed holders and never had any intention of taking them out as no need to.
 
I can't see any of the posts with incorrect terminology or am I missing something here !
 
To verify that an earth path exists
•Main switch off
•Disconnect earthing conductor from main earthing terminal
•Put one lead on the earthing conductor and the other lead on incoming supply line conductor
•Reconnect earthing conductor to main earthing terminal.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
testing ze on a shared supply cable.
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
14

Advert

Thread statistics

Created
julianacb,
Last reply from
Zorro,
Replies
14
Views
1,961

Advert