Sorry to put this up as I do not have enough information, just after some thoughts really.
Have a house where they want some additional sockets and looking at the CU (16th edition) there are two 16A circuits with two cables (2.5mm2) coming out from each, OK I thought two 16A RFCs, bit odd.
In the kitchen there are three double sockets, I have only looked at two of them, one appears to be part of a "ring" and connected correctly the other double socket has only one cable connected and the other cable has been cut short but is still live (more on this later) just the bare ends snipped off (unsleeved earth still there but not connected). I have terminated the ends and sleeved the earth so they are not exposed.
On using a voltage tester at this socket (indicating 110-150,220-250,380-500)
from the connected earth only:
to unconnected line 110V
to unconnected neutral 230V
to unconnected earth 230V
Since this was just a visit to estimate I stopped there.
The customer has had no problems with the sockets! and had PIR (electrical wiring check?) done a few years ago and everything was apparently OK! (I have not seen the report).

I am assuming that when they had a CU change (I think ten years ago) there were problems with L-E and L-N connections and the installer split the ring to two radials in the same breaker and dropped the breaker to 16A (possibly half of 32A?).
However I cannot reconcile the voltage indications. OK earth line fault so 110V to the other line. Possibly a reversed polarity somewhere and and another "line" earth fault to give the 230V between connected Earth and unconnected earth / neutral.
Anyway what do you think? Thanks

I will go back to them to say I need to check further and see the PIR report, but just confusing at the moment without further investigation.
 

Reply to 16A ring oh no its a radial in the Australia area at ElectriciansForums.net

Similar Threads

hi....im running cable for a split type 1.5 hp aircon....i have a roll of english 2.5 twin & earth, is this ok for the job? im running it to the...
Replies
0
Views
268
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
664
I would like to reuse a 10mm cable to provide a ring circuit in an area. The cable is currently used for an electric shower, still connected at...
Replies
10
Views
398
Hi guys, newbie posting! Does the following sound ok... Existing circuit: SOCKET on a ring -> spur to SWITCHED 3A FCU -> SWITCH -> hardwired FAN...
Replies
11
Views
739
Hope you're all well . I've had ring door bell 2nd generation hardwired for 1.5 yrs... it was connected to transformer which is connected to the...
Replies
22
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock