Sparks321

Hi, gone to look at a board change job, it’s an old re-wirable fuse box less than 3m away from DNO and ran in 16mm tails, 10mm earth and no bonding to the incoming gas pipe and customer has no idea where the water comes in as the house has no stop cock. I will be putting a dual split rcd 100a main switch board in. My question is, is it good practice to upgrade the tails to 25mm and earth to 16mm?
 
Depends on the size of the incoming fuse
 
Yeah that’s the thing i’m not sure of as it’s sealed. Suppose i could take apart to look.
 
Hi, gone to look at a board change job, it’s an old re-wirable fuse box less than 3m away from DNO and ran in 16mm tails, 10mm earth and no bonding to the incoming gas pipe and customer has no idea where the water comes in as the house has no stop cock. I will be putting a dual split rcd 100a main switch board in. My question is, is it good practice to upgrade the tails to 25mm and earth to 16mm?
What's the earthing arrangement bud?
What's the load?
 
Picture of the cutout would be good, there is a reason to my request.
 
W

What’s the reason?
Some cutouts are only 60A, with small ME fuse just a chance, but then you said 25mm tails so forget what I said.
 
Some cutouts are only 60A, with small ME fuse just a chance, but then you said 25mm tails so forget what I said.
Yeah 25mm from dno to meter then 16mm. Bit odd i thought. No harm in upgrading I suppose even if it is a 60a
 
Yeah 25mm from dno to meter then 16mm. Bit odd i thought. No harm in upgrading I suppose even if it is a 60a
I would if it were me.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
16mm meter tails
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
11

Advert

Thread statistics

Created
Sparks321,
Last reply from
7029 dave,
Replies
11
Views
2,231

Advert