If the suppliers meter tails are 16mm, do I have to use 16mm for a consumer unit on the consumer side or is it ok to use 25mm still?
 
Depends on the main fuse protecting the installation.
I’m guessing it’s 60/80a with that size existing tails?
 
It’s still ok to use 25 if that’s all you’ve got. Nothing wrong with oversizing.
 
16 for 16

25 for 25

have on occasion used 25 with 16 but only when I have run out of 16
 
I always install 25, that way it covers you if someone installs a 100 amp cutout fuse and makes it possible for DNO to upgrade the supply if needed for EV and the like
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Broxbourne
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
16mm suppliers tails
Prefix
Forum
UK Electrical Forum
Start date
Last reply date
Replies
4

Advert

Thread statistics

Created
Snailspark,
Last reply from
newfutile,
Replies
4
Views
1,628

Advert