have come accross kitchen job where x 2 ovens are on a lollipop circuit.
6mm t/e from csu to 45a dp switch and then small 2.5 t/e ring with 2 oven outlet plates.
each oven only 2.4kw max.
question is if tested ok, ie zs and ring end to ends, is this ok to leave as is?
 
What size is the protective device.
 
You will be pushing the 2.5mm cable close to it's limits,
So you may just scrape it in.
consider a protective breaker at the switch to protect the 2.5mm cable.
 
Thanks for that. Could not see any reason to change but first occasoon on a lollipop circuit so a little self doubt crept in.
Thanks again
 
  • Like
Reactions: Leesparkykent

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
.
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)
If other, please explain
.
Business Name
.

Thread Information

Title
2 ovens on lollipop circuit
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
5

Advert

Thread statistics

Created
sidekick,
Last reply from
sidekick,
Replies
5
Views
1,231

Advert