T
Toneyz
To sum it up we all think it is bad practice but not directly against the regs.
No I don't I think it's against the RegsTo sum it up we all think it is bad practice but not directly against the regs.
The joint box can effectively be considered as a socket on the ring. Only one unfused spur should be taken from a single point on a ring circuit as prescribed in appendix 15 the fact that’s it’s informative bears no weight on the argument as says that the design shown fulfils the requirements of 433.1
View attachment 45067
Appendix 15 is informative, and it says if you follow this appendix, you will meet the requirements of 433.1. However, it is NOT prescriptive, there may be other means of meeting 433.1 that are not covered by this diagram.
You don't have to "ram" 4 connections into each terminal, nowadays many (most?) of us are using maintenance-free connectors (Wago, etc.) that have 4 or 5 terminals, and are rated to 32A or more.
It says “this appendix sets out options for the design for ring final circuits in household and similar premises in accordance with regulation 433.1.”There is none, and what has been done is fine, if slightly unorthodox. Lots on here quoting appendix 15 as having some god like status, but it's only a guide, hence uses terms such as 'this can generally be achieved by' I.e. follow this and you don't have to think, all will be well. Think outside the box and all will still be well, provided you've thought, not guessed! In this case the op might have guessed but got away with it!
I’m not just trying to be argumentative I genuinely believe that it isn’t allowed.Appendix 15 is informative, and it says if you follow this appendix, you will meet the requirements of 433.1. However, it is NOT prescriptive, there may be other means of meeting 433.1 that are not covered by this diagram.
You don't have to "ram" 4 connections into each terminal, nowadays many (most?) of us are using maintenance-free connectors (Wago, etc.) that have 4 or 5 terminals, and are rated to 32A or more.
Ok, but where in 433.1 does it preclude taking two spurs from a single point on a ring final circuit?
It doesn't have to say that specifically, you just have to meet it. Just because they gave a few options for free doesn't mean that's exhaustive. If you follow the guidance, you will definitely meet the regs, if not, you have to decide for yourself.where does it say there may be other means of meeting 433.1?
actually it specifically states they have to be copper conductorsIt doesn't say you shouldn't wire a banana form a junction box to a tomatoe in a ring final, dies that mean you can.
Fair enough I’d be inclined to follow the regs though that way if you ever did end up on the chopping block you just point out the note at the front of the regs about complying with EAWRIt doesn't have to say that specifically, you just have to meet it. Just because they gave a few options for free doesn't mean that's exhaustive. If you follow the guidance, you will definitely meet the regs, if not, you have to decide for yourself.
This is a very common pattern also used in all parts of the building regulations nowadays. The building regs just say something very hard to use, and the Approved Documents give specific examples that should cover most situations.
C3 not to current standards citing reg 433.1 and mention Appx 15.Let me ask the question in another way...
You've just been asked to inspect the OPs property for an EICR and you find this junction box, it's been changed to a maintenance free one so that's no longer an issue.
How would you code the fact there are two spurs taken from the one junction box and what regulation would you quote to substantiate that coding?
c3 is actually "improvement recommended" (as it would improve the safety of the installation) According to Electrical Safety Council’s Best Practice Guide 4,C3 not to current standards
Nice catchc3 is actually "improvement recommended" (as it would improve the safety of the installation) According to Electrical Safety Council’s Best Practice Guide 4,
View attachment 45070
So in fact, even if it were non compliant, it shouldn't be the subject of a classification code unless it affects the safety of the installation.
Very rare I disagree with your stance on electrics but I think your enterpretation based on if it doesn't say you can't do something in the regs then you can do it.
It doesn't say you shouldn't wire a banana form a junction box to a tomatoe in a ring final, dies that mean you can.
433.1 says what you can do.
C3 not to current standards citing reg 433.1 and mention Appx 15.
I think the wording is quite clear in saying that Appx15 is showing the design options. As in the options on how to spur from a ring rather than the diagram being one of many different options.
Out of interest how would you justify not coding it?
id still C3 it because it could affect the safety of an installation there may even be an argument for a C2 because it could be potentially dangerous,in the event of an overload
In that case it may well be technically compliant because there isn’t a reg forbidding it so it’s wrong because it just isThank you for those kind words.
I think my hard line stance makes it come across that way, but that's not really what I'm getting at.
In the course of this thread, I've read 433.1 several times and it makes no mention of junction boxes. It's focus is on cable loadings and ensuring that they are adequately protected against overload through the correct selection of cable size and appropriate OCPD.
Specifically 433.1.204 states the rules for cable sizing for ring finals.
Since these two spurs are designed correctly, i.e. the correct size cable and only one double socket outlet on the end of each, the spurs themselves comply. The ring final itself complies because it is wired in an appropriate cable and protected by an appropriate OCPD.
So the three elements here comply in their own right. Providing the junction box used can handle the expected load (whether or not this is accessible is another discussion), there is no reason that I can see how this arrangement can be deemed to be a non-compliance.
The appendix 15 argument if taken to it's logical conclusion means you can never have a single socket outlet on a ring final, or take a spur from the origin, or have more than two double socket outlets after a fused spur, or have a grid switch system... why? Because they aren't shown on the diagram. The diagram provide guidance on how to comply, it's not a definitive list of what you can do (as it states, the diagram shows options).
And part of why I'm taking a somewhat hard line stance is because I'd like to see more substantiated 'it's against regs'. If I make statements to that effect I try and provide appropriate regulation numbers as it may help someone understand more. And in this case, no body has been able to explain to me how this arrangement doesn't comply without resorting to the appendix 15 argument.
I was thinking more overloading the actual junction box itself rather than the wiring... but I do see your point potentially anything could be plugged into any socket and cause an overload anywhereNooooo! Not the overload argument again!
There is no more risk of overload with what the OP has done, than with two spurs taken from different points on the ring. Subject to the junction box making a sound connection, which is a caveat we've been accepting all along.
I will state categorically that this method is just as safe as any other. The only debate is about whether it technically complies as a configuration, which I think it does.
Ok, but where in 433.1 does it preclude taking two spurs from a single point on a ring final circuit?
That's all I'm asking.
I can't find a regulation that precludes it, but I'm happy to be proved wrong because then I'll have learned something new![]()
Let me ask the question in another way...
You've just been asked to inspect the OPs property for an EICR and you find this junction box, it's been changed to a maintenance free one so that's no longer an issue.
How would you code the fact there are two spurs taken from the one junction box and what regulation would you quote to substantiate that coding?
Bet you will as wellI feel like an apprentice again, or worse a Electrical Trainee.
I’d grade it with a squiggle that cant be deciphered - I’ll make it look like a 1,2,3 and a tick, maybe even a N/A to cover all basis.
I’m off to bed. If I dream about spurs, I hate you all.
Sparkychick, like your clarity on this.
I think that’s the absolutely wonderful thing about the regs. They are open to interpretation so we are probably all wrong it’s really only down to yourself and how you justify it that makes it right or wrong everything is right if you can justify it.Thanks hon, but don't get too enthusiastic, I could be wrong![]()
I think that’s the wonderful thing about the regs. They are open to interpretation so we are probably all wrong it’s really only down to yourself and how you justify it that makes it right or wrong everything is right if you can justify it.