I’ve worked on 660V & 550V systems. Where you are just dealing with motors and not bothered about Fred needing 230V for his kettle, higher voltages mean smaller cables. OK if you needed 230V you had to put in a small transformer.
Every plant I worked on as an apprentice was 550V. I was involved with installing a new plant, it had got this weird voltage 433V! Some of the old guys didn’t know what to make of it, 230V without a transformer??? Just to add to the fun, after a few years the systems expanded so some areas had both 433 & 550 side by side.
Think about it, a 200A feed at:
433V = 150KVA
550V = 190KVA
660V = 230KVA
They all use the same grade of cable
Every plant I worked on as an apprentice was 550V. I was involved with installing a new plant, it had got this weird voltage 433V! Some of the old guys didn’t know what to make of it, 230V without a transformer??? Just to add to the fun, after a few years the systems expanded so some areas had both 433 & 550 side by side.