Hi there...

Bit out of practice with 3phase design, and want to learn more.

Just want to check if this would be correct:

Ib = KW/V*1.732

Many thanks,

Sy
 
Hi there...

Bit out of practice with 3phase design, and want to learn more.

Just want to check if this would be correct:

Ib = KW/V*1.732

Many thanks,

Sy

Yes, as long as there is no power factor :)
and watts not kW

The equation you are rearranging is actually
total power(W) = √3*Vl*Il*PF

you are using Il to be your Ib value and Vl = 400
 
Last edited by a moderator:
Thank you for your help there,

Power factor will definately be invloved in the example I'm looking at.... as it has a motor.

Time for a bit more investigation, I will probably be back:)

Cheers Sy....
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

sythai

Arms
~
Joined
Location
Devon, United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
3phase help please....
Prefix
N/A
Forum
Electrician Talk | All Countries
Start date
Last reply date
Replies
4

Thread Tags

Advert

Thread statistics

Created
sythai,
Last reply from
sythai,
Replies
4
Views
1,431

Advert