Discuss 400 amp bs88 in the UK Electrical Forum area at ElectriciansForums.net
ganzo
Hi
We have a LV section board supplied with 630mm singles. The ammeter on the board is reading 530 amps per phase. We checked upstream and it is supplied from 3x400amp bs88 fuses. Can anyone explain why the fuses can take this load without blowing. If so where can I get some documentation to back this up.
You need the time/current curve for a 400amp bs88-2 at 530amps it will be unlikely to blow the fuses straight away but after a good duration ... I doubt this is a average demand you measured or they would have been taken out by now.
I will assume you have a calibrated clamp meter.
Check the max Kwh demand on the meter by cycling the button most let you do this...
How exactly are you measuring this value?
What is the max that a 400amp fuse could cope with?
Your not reading my replies as this is a overload their isn't a max you can apply you look at the current/time curve for the fuse and it will give you how long in seconds the fuse will hold for if that current is maintained.
If you are correct and this current was maintained the fuses will operate - what is the average value on your meter and again with what and how are you measuring it, and are you doing it correctly. I ask because like most you fail to fill your profile in so we have to ask you in simple terms as we can't guess your experience and qualifications.
The load is fluctuating as its a waste transfer site with lots of motors. There is a lcd display on the main incoming section where you can select kw amps or volts. I say 530 amps average per phase as the display is changing constantly.
Reply to 400 amp bs88 in the UK Electrical Forum area at ElectriciansForums.net
I'm in the middle of preparing a quote for installing 12 x 3Kw and 4 x 2Kw halogen heaters in a church. The system design was provided by a...
On an EICR I found a 200 amp 3ph supply, TNS earthing (which looks original) and Ze of 19 ohms. No rods. No RCDs. L1 -> N was about 0.5 ohms...
I've a 3 phase storage heater currently wired to the main fuse box in an office I have. The heater has 2 supplies/isolators, 1 for charging at...
So far I have never had to deal with a new supply but a possible site we are looking at will need some major changes and so I wondered if folks...