What would of stopped this happening?

Job I did this morning.

SWA supply for outbuilding had sliced basic insulation at the gland due to poor wire stripping. Another outgoing SWA feed for an external GYM was actually back feeding water into the consumer unit as it was uphill and had some head pressure of about 4 metres on the cable. The gym had a rotary switch with some plastic 20mm conduit directly above the SWA coming in so the SWA was simply funnelling water downhill into the main outbuilding C/U!

Anyway water dripped directly onto sliced conductors where it arced and roasted the insulation. Main 80a fuse didn't blow
though.

Ah. Also. The armour wasn't terminated at the metal consumer unit. It had been terminated outside and the earth bought in with a separate fly lead. The Gland for the 2 SWA conductors was plastic so no earth fault occured at the gland when the water caused the arcing. The cable WAS RCD protected.

Wondering if there is such a thing as an AFDD master fuse or switch? What's the maximum AMPerage of these things?

Cheers

Spynage
 

Attachments

  • IMG_20221224_103809.jpg
    598.5 KB · Views: 40
  • IMG_20221223_122310.jpg
    416 KB · Views: 40
  • IMG_20221223_121809 (4).jpg
    420.7 KB · Views: 39
Last edited:
The armouring of swa only needs to be earthed at one end, so long as there is a path back to the MET. although it’s very rare you’ll see that, and also a bit “rough”

I’m pretty sure that an RCD usually wouldn’t trip on a live-neutral short as there’s usually no imbalance in the loads of the 2 conductors, and the rcd is (usually) only looking for imbalances of more than 30ma… in practice, chances are that cable would smoulder away all day long.

Another thing to note is that it might not even be on an rcd, especially with it being a sub-main installed in armoured cable. The earthing arrangement of the installation can also play a massive role when it comes to RCD operation.

Main fuse definitely won’t have blown if the breaker supplying the cable didn’t.

If you had a master AFDD at the source, then a fault like that would have wiped the power to the complete installation. Which most likely wouldn’t be ideal.

You can protect individual circuits/submains using AFDD’s, for instance, if you had an AFDD at the starting end of the submain in question, you’d of lost power to the DB that the submain itself feeds, and you wouldn’t be able to regain that power until either the fault is rectified or the AFDD is removed. A lot of firms now produce AFDD/RCBO’s, but they’re still very expensive.
 

Reply to AFDD for main supply? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
726
Afternoon All, Just pricing up a job and thought I'd pick your brains. Quick run-down, Block of Flats with an underground car park. In the...
Replies
27
Views
2K
Hi all, Been browsing these forums for a while, always great to learn a new way to skin the same cat. Anyway, cut a long story short, was an...
Replies
11
Views
630
Hi I've inherited a very tight space, a KMF switch and some split-con for a sub-main to try and tidy up. It's a joyous non-restrained single...
Replies
3
Views
193

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock