Just about to start pulling in the cables for my smile detectors, however I dint have the detectors yet. Is there enough room in the terminals to terminate a supply feed in and then loop out to the next detector or is a junction box required to house the feed and a supply taken from every J/B?
 
I think there's enough room.
This video by JW shows early on the connection area which i believe is common to all AICO units...I have some smokes and a heat and they all look the same, but mine are wired as to 1 hard-wired in hall, and the rest radio-linked.
View: https://www.youtube.com/watch?v=UD5BWg-OmQM
 
I used to put a round dry line box behind Aico alarms, otherwise the wires were exposed from the sheathing, if you get my drift.The mounting plate is quite thin.

PS I would include an isolator switch in your installation.
 
I used to put a round dry line box behind Aico alarms, otherwise the wires were exposed from the sheathing, if you get my drift.
They are not exposed, there’s a cover over the cables, there’s no cables exposed once the smoke head is removed.
I think you’re thinking of the wrong manufacturer
 
  • Agree
Reactions: Leesparkykent
They are not exposed, there’s a cover over the cables, there’s no cables exposed once the smoke head is removed.
think hemeant where the cables enter from the back. you need to keep the sheath stripped part quite short.
 
  • Agree
Reactions: Jim_e_Jib
i'd not call this loads of room when you have a T/E and a 3C/E in there. just about enough.
1595951486790.png
 
Loads of room! My house is smaller than that!
Oh, wait...maybe that's not to scale? :)
 
me neither, but you need to strip back no more than 1" of sheath. or it's difficult to get the cover on. that's probably why i find a few knocking around the bottom of my toolbelt. :)
 
me neither, but you need to strip back no more than 1" of sheath. or it's difficult to get the cover on. that's probably why i find a few knocking around the bottom of my toolbelt. :)
Best smokes on the market in my opinion.
They’ve never seemed to have changed much over the years.
 
funny that. last week replaced a duff one. bungalow only had 2, both square. tight fisted client would only stretch to replacing the faulty one, then complains he can't obtain a square one and the new one exposes the 30 year old patch of wallpaper on the ceiling that was under the detector. still allcredit to aico for making them compatible with ancient ones.
 
funny that. last week replaced a duff one. bungalow only had 2, both square. tight fisted client would only stretch to replacing the faulty one, then complains he can't obtain a square one and the new one exposes the 30 year old patch of wallpaper on the ceiling that was under the detector. still allcredit to aico for making them compatible with ancient ones.
I could never get the rectangular type smokes square haha
 
  • Funny
Reactions: telectrix
My point is, can you get x2 t+e cables terminated in it? Feed in and feed to next detector?
 
My point is, can you get x2 t+e cables terminated in it? Feed in and feed to next detector?

Yes, even I have managed it easily with 2×3&e.

Can't leave long tails though, just an inch or so.

Are you using twin, or three core - need the third line wire for inter-operation /linking of alarms. (Unless paying for the additional wireless option)
 
Yes, even I have managed it easily with 2×3&e.

Can't leave long tails though, just an inch or so.

Are you using twin, or three core - need the third line wire for inter-operation /linking of alarms. (Unless paying for the additional wireless option)

Sorry, I meant 3c+e
 
Does everybody use 1.5mm for their dedicated smoke detector circuits?
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

gazdkw82

Arms
~
Joined
Location
leicester
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
Aico smoke detector wiring
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
59

Advert

Thread statistics

Created
gazdkw82,
Last reply from
Mike Johnson,
Replies
59
Views
13,545

Advert