Scotchydog

I have my am 2 comin up and its on a 3 phase board (TNC-S) my question is when doing the live tests first i would do the Ze with the high current 23A setting (Megger LT7) between each phase and removed main earth (main switch off and on supply side) then work out Zs = Ze + (R1 + R2) and use table 2D in on site guide for compliance then do i

set the megger to pscc and test between each phase and neutral, then each phase to earth (not phase to phase) (and with main earth back in place) and then which ever is the highest reading double it then write the result in the pfc at top of page(bs7671 test results)

Thanks
 
Last edited by a moderator:
the best way of doing insulation resistence test would really appreciate this as well-

apart from pulling the fuses out of 2 neon spurs (theres also one on a smoke detector but it doesnt have a switch or a neon) putting smoke detector in chock blocks putting light fitting in chocky blocks and removing live out of ring mains rcbo. rest are just mcbs and theres no rcd, also my lighting circuit (2 way and intermediate) i think its on L3 do i just flick the switches(for strappers) only between L3-n L3-e.

last i have a 3 phase motor cicuit from db to DOL starter then to motor(actually its box with prong holes in labelled motor) do i have to put the cables from db (to dol starter) in chocky block or is it ok to megger them and same with DOL starter to motor box if i megger through the prong holes do i have to put the cables from the DOL in a chock block or just megger them connected

thanks
 

Reply to Am2 - testing questions, pscc in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I have been asked to look at this report as the customer has been given (in their words) 'A very high quote plus VAT'. It doesn't look well...
Replies
5
Views
599
I want to check the insulation of the 3-phase 400VAC asynchronous squirrel cage motor. Motor's stator windings are connected in delta. I've read...
Replies
10
Views
2K
Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...
Replies
5
Views
1K
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K
Hi everyone Recently I have come across an advert of someone selling Afdds C type and the person mentioned the need to sell because Zs was too...
Replies
16
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock