Discuss Are the bloody Regs statutory or not? in the UK Electrical Forum area at ElectriciansForums.net

oracle

-
Esteemed
Arms
Reaction score
413
As of 1 January 2005 it is a legal (statutory) requirement for all work on fixed electrical installations in dwellings and associated buildings to comply with relevant standards. The relevant UK standard is BS 7671 2018 (Non statutory)

The EAWR (statutory) says that compliance with BS7671(Non statutory) will mean compliance with it.

The Building Regulations (statutory)

Approved Documents are intended to provide guidance for some of the more common building situations. However, there may well be alternative ways of achieving compliance with the requirements. Thus there is no obligation to adopt any particular solution contained in an Approved Document if you prefer to meet the relevant requirement in some other way.

So where does that leave us? Best is stick to the Regs and treat them as statutory (even though they're not) and you can't go wrong. They are the code we live by.
 
If you stick to the relevant British standards in whatever work you undertake be it fire alarms,emergency lighting and electrical installations then you can’t go wrong.
 
I sometimes think they left it like this to ensure IET retain copyright and revenue for these regs - if they were l-a-w they'd need to be freely available I think (?).

Ah, I remember these discussions now.
I came to the conclusion that if the Regs were 'Law', they would be at least 10 times bigger. They'd have to be total water tight without a single loophole in them. You'd need to be a trained lawyer to understand them. No 30 hour training course to get your 18th :D
 
It's comparable to the ISITEE position, where people often ask "Do you have to have portable appliance testing by law?" Of course, you don't, however you do have to comply with EAWR. Following the Code of Practice 4th Edition is the recognised and established way to maintain equipment and as far as is reasonably practicable, prevent danger.

There may be other ways to achieve the same end result, however (a) why try to reinvent the wheel? and, (b) there is a likelihood that said reinvention would appear wheel-like and closely resemble the existing CoP...
 
Pete, get a grip and lay off the Mogadon
I stated 3 times that they are not statutory, it's just that the EAWR and Part P think they are.
Just adding my pennies worth no need for derogatory replies Mate, Oh sorry forgot you are the oracle after all didn't mean to spoil your thunder.
 
Last edited:
This is the old logic chestnut.
A implies B is a known fact.
From that it does Not follow that B implies A
In this case compliance with bs7671 implies compliance with part p. But compliance with part p doesn't imply compliance with bs7671.
 
Why does everyone think Pete is ****ed when he gives an incoherent reply?
Don't think he is thinking I'm P//sed Ant just taken a sleeping tablet. Maybe he just needs to take stock of what he is saying, thanks for your support anyway.
 
Just adding my pennies worth no need for derogatory replies Mate, Oh sorry forgot you are the oracle after all didn't mean to spoil your thunder.
What derogative? You're the one who said you use Mogadon as a recreational drugiin another post after all.
Lighten up, it's just one old Fart taking the pi$$ out of another.
 
Last edited:
What derogative? You're the one who said you use Mogadon as a recreational drugiin another post after all.
Lighten up, it's just one old Fart taking the pi$$ out of another.
Deleted
 
Last edited:
fine mate. just woke up for a smoke and a brew. letting dogs out for wee wees.
 
mother is fine.4 healthy pups, all putting weight on day by day.

3weeks.JPG
 
BS 7671 is not statutory as a stand alone document.

However; Building Tegulation state BS 7671 in terms of what to follow and they are law so in effect not following BS 7671 will lead to non-compliance to Building Regulations and possible legal consequences.

Also if a customer states to install to BS 7671 and you agree to take on the work this then becomes a binding contract and you are legally obliged to deliver on it or you could be sued.

In conclusion, BS7671 is indirectly a legal document.
 
Building Tegulation state BS 7671 in terms of what to follow and they are law so in effect not following BS 7671 will lead to non-compliance to Building Regulations
This is incorrect. The approved documents refer to bs7671 as a possible way to comply but nowhere in the regulations themselves does it mention them.
Part p the actual part on the statute is very simple:
"Reasonable provision shall be made in the design and installation of electrical installations in order to protect persons operating, maintaining or altering the installations from fire or injury."

Also a contract with a company or customer adding for bs7671 is not in statute that's just a contract and comes under different law
 
This is incorrect. The approved documents refer to bs7671 as a possible way to comply but nowhere in the regulations themselves does it mention them.
Part p the actual part on the statute is very simple:
"Reasonable provision shall be made in the design and installation of electrical installations in order to protect persons operating, maintaining or altering the installations from fire or injury."

Also a contract with a company or customer adding for bs7671 is not in statute that's just a contract and comes under different law

I never mentioned Part P and your last paragraph is exactly what I said.
 
My view is that it's basically irrelevant. If a court has to decide if you caused the deaths, or did not, then they will compare your methods to whatever the closest textbook is for the 'right way'.

So if the regs say do 'a', and you went and did 'b', in the view of the court that's where the error was. We can assume the court will not be able to fully understand the nuances of the situation, so will inevitably resort to the nearest rule book they can find.

working out what is technically a legal requirement isn't very useful. In the end, all that matters is being on the right side of what people will ultimately judge as correct, if you were ever to find yourself in that position.
 
Are you suggesting Part P does not form a part of the Building Regulations?
Part P of the building regulations is part of the building regs, and approved document p includes the building regulation on the tinted background, together with non statutory guidanceo onways of complying.
For practical purposes it doesn't really affect what we would do, but given the whole title of the thread is about whether the bs7671 is statutory it's a critical distinction.
 
Although a keen supporter of working to BS7671, I have to say that a safe installation could be done without referring to it, using that rare thing these days, common sense. I still find it rather strange that there is a general opinion that if BS7671 isn't strictly adhered to them death and a court case will follow
 
We can assume the court will not be able to fully understand the nuances of the situation, so will inevitably resort to the nearest rule book they can find.
The court is not an expert in most things really, that's why they call witnesses who are experts. It's a normal practice. I am guessing we would be in chaos pretty quickly if courts made important judgements based on no professional knowledge.
 
Although a keen supporter of working to BS7671, I have to say that a safe installation could be done without referring to it, using that rare thing these days, common sense. I still find it rather strange that there is a general opinion that if BS7671 isn't strictly adhered to them death and a court case will follow

I would not say there is a ‘general opinion’ as you put it. I would say that in terms of taking out an ‘insurance policy’ following BS7671 is the safest and most sensible way to protect yourself, your family and your home ‘should’ the worst happen.
 
Last edited by a moderator:
Although a keen supporter of working to BS7671, I have to say that a safe installation could be done without referring to it, using that rare thing these days, common sense. I still find it rather strange that there is a general opinion that if BS7671 isn't strictly adhered to them death and a court case will follow

Common sense is not PC apparently. It's far easier to just have a textbook approach. Personally though, I would rather all money spent on regulation of just about everything was instead spent on nurturing common sense in people through school!

Anyway yes, if something is safe, then it doesn't really matter if it complies or not. If it's truly safe, then it will never need to be examined to prove otherwise.
 
The court is not an expert in most things really, that's why they call witnesses who are experts. It's a normal practice. I am guessing we would be in chaos pretty quickly if courts made important judgements based on no professional knowledge.

Yes but in the end the court makes the decision. It's unlikely that in the time allowed the final decision maker(s) could really understand enough about what was said by any party to really appreciate the technicalities. It's fine if it's an obvious contravention of safe working practice. But many cases will be far more complicated.
 
Yes but in the end the court makes the decision. It's unlikely that in the time allowed the final decision maker(s) could really understand enough about what was said by any party to really appreciate the technicalities. It's fine if it's an obvious contravention of safe working practice. But many cases will be far more complicated.
I realise there are time pressures but the judicial system is mostly set up to avoid miscarriages of justice. The legal system gets a bad name due to ambulance chasers getting settlements out of court before hand.
by way of example of the legal process trying harder where things are more complex the Grenfell tower inquiry (part 1 of 2) has been sitting for about 6 months so far, and has heard evidence from academics and other experts on various aspects of the situation.
To be honest you could have a perfectly bs7671 compliant installation and given the number of debates on here there's a good chanch the prosecution could find an electrician to give it codes left right and centre.
And on top of that even the regs allow deviations.
 
I realise there are time pressures but the judicial system is mostly set up to avoid miscarriages of justice. The legal system gets a bad name due to ambulance chasers getting settlements out of court before hand.
by way of example of the legal process trying harder where things are more complex the Grenfell tower inquiry (part 1 of 2) has been sitting for about 6 months so far, and has heard evidence from academics and other experts on various aspects of the situation.
To be honest you could have a perfectly bs7671 compliant installation and given the number of debates on here there's a good chanch the prosecution could find an electrician to give it codes left right and centre.
And on top of that even the regs allow deviations.

That's prety much my point. I may have worded it badly reading back...

But in essence if it's truly safe, you won't have to argue your case in the first place.

The regs exist so that people without the common sense to work safely have a framework they can simply adhere too. It's in the book = safe.

But I would argue that the safest person of all is the one that respects the books, but is ultimately driven by their own knowledge of what is safe, and why.
 
Personally, to summarise, I would say that there is 'The Law'. which you have to comply with. Then there are a subset of 'Regulations' and 'Standards' etc. that you have to adhere to, to comply with 'The Law'.

eg, if you left a naked live cable flapping around, you're guilty!
i.e. there is no law, as such, that you can leave a bare live cable for anyone to touch, but you'd be going down if they did!
 
Last edited by a moderator:
Personally, to summarise, I would say that there is 'The Law'. which you have to comply with
Correct
Then there are a subset of 'Regulations' and 'Standards' etc. that you have to adhere to, to comply with 'The Law'.
Depends if the regulations are statutory eg the gas regs are but the electrical regs aren't.
there is no law, as such, that you can leave a bare live cable for anyone to touch
Correct, building regs would be less relevant here, that would come under negligence laws even assuming it wasn't done intentionally to cause a danger.
 
Memorandum of Guidance on the Electricity at Work Regulation is also supportive. Why don't they make the whole lot Statutory, included in the main body of text ?
 

Reply to Are the bloody Regs statutory or not? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi fellow sparks, I've just started out on my own so I'm spending a lot of my time trying to find out the correct way of doing things of...
Replies
13
Views
958
Hi guys, I've gotten AI to write up a terms and conditions for my company and then went through it with AI and tweaked it to make it sound a...
Replies
3
Views
464
I've just stumbled across the below elsewhere online, anyone aware of it? PRESS RELEASE: ELECTRICIAN’S GUILTY PLEA OVER REPORT SIGNING OFF...
Replies
40
Views
6K
Morning all So the site I'm based at recently had some work done (think partitioners). This package of work included electrical. This was...
Replies
47
Views
8K
Hi all We've had some works done in our kitchen which has involved fitting a new cooker circuit, installing some downlights to replace ceiling...
Replies
12
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock