well....it was actually for that shanky article to work out....Even if you use long lead method (R2) to calculate cpc, you still have to 'power down' to determine R1 and Ze - you may as well just invent a figure for Zs, jot it in the form and be on your way lol
however R2 is adequate for condition reporting...together with Zs...so by means of a breakout box/prods as required...you wouldn`t need to power down...would you....i just wanted to see if he could work it out...
you would need to power down for your end to ends (ring) and IR as usual but....using this method you cause minimum disruption ...