I'm testing street lighting which has 10 sodium lights over a space of about 200m wired in 3 core 4mm armoured underground, this is protected by a 16 amp mcb. I've done a Zs and its greater than the max Zs values for the 60898 type b, what is the easiest way of working out the load.
 
what rating are each of your lamps in the fitting?

Find out how many lamps you have on the circuit in total and find the total rating of the circuit in Watts (Power)

Power / Voltage = Current.

so say each lamp was 200Watt

2000/230V - 8.69Amps.
 
UM, well that could be a problem, I would bet 10 sodium street lights over 200 mtrs of cable would trip haha, m1ck, whats the ZS reading?
 
Zs reading was 3.64 and it has a contactor I was thinking of down grading to a 10 amp that's why I wanted to work out a accurate load
 
I'm testing street lighting which has 10 sodium lights over a space of about 200m wired in 3 core 4mm armoured underground, this is protected by a 16 amp mcb. I've done a Zs and its greater than the max Zs values for the 60898 type b, what is the easiest way of working out the load.

Hi M1ck,

I don't want to seem rude but you are testing street lighting yet asking on a forum how to calculate design current?
 
whichever way you work it out don,t forget the power used will be a little more than the 70W stated for the lamp,due to losses in the control gear etc,on a single lamp this may not matter but on a run of them well it may be something you need to allow for.
 
A Test with clamp on amp meter with all the lights running will soon give you the full load,but if the lamps are 70watt the load will be well under 10amps in which case you zs of 3.64 will be fine with a 10amp type B or you could go to a 6amp type C
 
Test with clamp meter and assess load in reference to the design current for the circuit.
Measure R1+R2.
Measure Zs at distribution board.
Measure Zs at circuit.
Look for any abnormal results across the above ^.
60898 Type B 6Amp or 10Amp will be fine IMO.
 

Reply to big problem in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
My garden lighting was tripping my MCB so I checked all the junction boxes outside. I disconnected the live, neutral and earth connections in...
Replies
2
Views
904
Hi Guy's, I'm revising for my 18th amd 2 and came across a question that has me a little confused. I think its probably the question is badly...
Replies
11
Views
2K
Need help check that my cable calculations are correct as still new to doing them. 6A Lighting Circuit 60898 MCB Type B wiring in 1MM²/1MM² T+E...
Replies
13
Views
3K
Just thought I'd share this quick sobering story that happened to me a couple of weekends ago.... Overhead 230v lighting festoon, LED golf ball...
Replies
5
Views
777

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock