Hi we are quoting for installing the main feed for a public swimming pool , its a 3 phase install with 3 no. 300 AMP main fuses . we will be installing a 315 3pn switched fused isolator then SWA on cable tray at a distance of 25 mtrs to the main board , i have allowed for 240 mm2 cable with 70 mm earth am i right or can i install smaller ???
 
Assuming it is XLPE it is plenty big enough. Can you install smaller, I would say yes. You not done any calcs then.
 
Hi we are quoting for installing the main feed for a public swimming pool , its a 3 phase install with 3 no. 300 AMP main fuses . we will be installing a 315 3pn switched fused isolator then SWA on cable tray at a distance of 25 mtrs to the main board , i have allowed for 240 mm2 cable with 70 mm earth am i right or can i install smaller ???

Need more info!

What's your design current, ambient temp and any other factors?!
 
Assuming it is XLPE
Unless you have switchgear etc. with terminals suitable for 90 degree operation then it being cross-linked polyethelene isn't terribly relevant.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Cable size check please
Prefix
N/A
Forum
Commercial Electrical Advice
Start date
Last reply date
Replies
3

Advert

Thread statistics

Created
Oliver Townsend,
Last reply from
Risteard,
Replies
3
Views
1,456

Advert