I have a run of cable where 12% is buried in ducts, the rest is on perforated tray, what are the limits on amount of cable buried when sizing cables?
Discuss Cable size when burying in the UK Electrical Forum area at ElectriciansForums.net
See Table 4D4A of BS7671.5m of 40m run , I was looking for a formula or guide value if there is one?
Is the cable installed yet or not? Information of max demand required? The difference between Ref E & Ref D can be quite a lot of derating or larger cable sizing.I have a run of cable where 12% is buried in ducts, the rest is on perforated tray, what are the limits on amount of cable buried when sizing cables?
NO it's not installed as yet, just sizing the cable required.Is the cable installed yet or not? Information of max demand required? The difference between Ref E & Ref D can be quite a lot of derating or larger cable sizing.
70mm 3 core x 2 swaIs the cable installed yet or not? Information of max demand required? The difference between Ref E & Ref D can be quite a lot of derating or larger cable sizing.