Discuss calculating Zs at socket outlets in the Industrial Electricians' Talk area at ElectriciansForums.net
V
voltage
Hi all
After some advice on measuring Zs at socket outlets using the megger 1553 what setting should the megger be on for this test ? i no i have to use the plug in plug i got with my megger just not sure what setting the megger has to be on ?
I no how to calculate Zs by calculation using Zs = Ze + ( R1 + R2 ) for radial circuits
But i would like to know how to measure it at socket outlets.
Any advice or help would be appreciated many thanks volt.
I believe that that meggar as 2 options the no trip and the normal EFLI test.
If your socket is RCD protected then you would use the no trip setting on the instrument.
If the socket is not RCD protected then the normal EFLI setting, or I think Hi on the megger, would be used.
plug in. set to hi or no trip. switch on socket. megger shows voltage then----------- then make yourself a brew while the megger clicks and farts and eventually comes up with a reading
And if it's a 'no-trip' reading, try it again for a different reading!
Make sure there are no loads on the circuit being tested, any 'noise' and the readings on 'no trip' become quite sporadic.
Hi all
Hello voltage
Where there is an RCD/RCBO protecting a final circuit then a no trip 3 wire test should be performed to obtain the Zs value.
For unprotected circuits a hi loop test with 2 testleads should used.
In the case of acquiring a Zs on a power circuit with standard sockets then the mains plug lead will be utitilised using either no trip or hi loop depending once again on circuit protection.
Regards
Megger TSG
Hello voltage
Regards
Megger TSG
Thank you
and have a good stock of AA alkalines. meggers eat batteries. you should have noticed when you switch on the megger, it shows the battery volts. if below 10v, replace.
You Zs should also be taken from the socket/accessory furthest away on the circuit.
yes, it should. the op is learning how to use the tester, not actually testing installations as yet.
Reply to calculating Zs at socket outlets in the Industrial Electricians' Talk area at ElectriciansForums.net
Im currently in my apprenticeship and completing an assignment that involves cable calculations. Im currently stuck on how to find the design...
Hi All, Any help would be greatly appreciated. When calculating the Zs for a circuit specifically for 2396 do you have to incorporate the on site...
Hi all, Just a quick one regarding the need for RCD protection for socket outlets rated up to and including 32A. I have been tasked to install...
Hi. Im looking for some advice when calculating submain cables. Basically there is a new connection of 80Amps that is to be used for a dwelling...
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...