JUST A WORD OF CAUTION AND POSSIBLE DANGER.

Although I have not tested the 'KEWTECH KEWCHECK 103 MAINS WIRING TESTER Ii have tested a variety of similar testers including an earlier version of the Kewtech tester and the similar Martindale tester. In my experience they all have a fundamental flaw as follows:-

If a socket you are testing has been wired reverse polarity and the earth pin is live. the tester will give the indication that the socket is wired correctly. This obviously is a dangerous situation.

Maybe I should explain further. we have all come across a socket that has been wired reverse polarity and maybe we have all come across a none existance earth for the sockets. The combination of these two faults fools the testerto give the indication that the socket is wired correctly. Needless to say this situation would make all class 1 items of equipment extremly dangerous and a risk of electric shock by touchig the metal casing, yet the tester has given the false indication that all is well.

I would welcome feedback regarding this subject.
 
What were the connections at the socket.Were they in the right connections:confused:I've seen this once before,the tails were connected the wrong way round in the CU.
 
Last edited by a moderator:
Hi Mac,

Quite simply the socket was connected reverse thus the live was in the neutral connection and the Neutral was in the live position. No earth was present and in fact the earth pin was live. Yet the tester gave the indication that the socket was wired correctly.
 
Last edited by a moderator:

Reply to Caution risk of danger and electric shock in the Australia area at ElectriciansForums.net

Similar Threads

Hi all. Sort of an interesting one. I had a call from a client to say she is getting a shock when using the shower. I told her not to use it and...
Replies
15
Views
1K
Hi all, New to the forum. I have been asked to look at this for one of our guys who's had an issue onsite after some electrical works had been...
Replies
4
Views
742
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
464
Hello all, Looking for help here as I've come across a strange call-out today. Bare with me here: Got a call from a customer saying they had...
Replies
13
Views
2K
Good afternoon all, today I experienced a near death electric shock. This happened on a single phase domestic property! I was carrying out a few...
Replies
15
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock