Evening all; I have just completed the C&G 2377 PAT test exam and now getting to grips with testing in the real world. The IET code of practice shows that class I devices can have unearthed metal parts so in the case of our clothes iron how do I tell if there's no earth continuity because it has a break somewhere in the cpc or just because the sole plate is otherwise insulated and not earthed (device not marked double insulated and definitely has earth connection inside plug)? Thanks for any feedback.
 
If there is no CLASS_II.JPG symbol then the COP states that it should be considered as Class I, since you have a cpc in the cable then there should be some metalwork accessible that needs to be earthed and if you get continuity to that point then you are OK.

I have found that some almost entirely plastic coated items often need a long probe into the interstices to reach the earthed metal work, a real nuisance.

If there is earthed metal work then you can test continuity from that earthed metal work to the sole plate and see if they are internally connected and this would bypass a cpc break.
 
I've found with a lot of irons there is a coating on the element which means you wont get a good earth.

Try the very tip in the gap between the sole plate and the body of the iron if you can fit your earth bond clip in there.

I've found a few coffee makers with ceramic heating elements and completely plastic casing, no exposed metal parts Just have to test as class 2 and make it clear in your notes.

The more appliances you test the more of a feel you will get for finding a good earth and sniffing out problem appliances
 

Reply to Class I device with unearthed metal in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

Similar Threads

I am a new PAT tester for a school, and I am stuck testing a plasma globe. It has a two core wire going to it, but no class 2 mark on the...
Replies
18
Views
2K
Sorry if this thread is in the wrong section, I was always led to believe that a TV was class 1 for PAT testing, however the TV has a metal earth...
Replies
8
Views
1K
Hi all, Disclaimer: I'm not an electrician and have very basic knowledge of electrical installation. We've been putting in a new kitchen into an...
Replies
20
Views
2K
I want to PAT a coffee machine. It has a sealed plug; no class 2 mark; a round cable that suggests twin and earth; and no visible metal. Please...
Replies
8
Views
2K
My Champion generator is set up (according to the manual) as having a floating neutral. The plan was to run a 16A commando hook up cable from the...
Replies
2
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock