Hi all, carried out an EICR recently on a caravan. System is a TT with 4293 100ma main switch then into a 3036 board. All wiring tested ok with just a few damaged accessories to change. RCD tested ok but its not time delay. Should I be recommending additional 30ma RCD protection for circuits (in walls, bathroom and outside socket)?
You should Code them appropriately. Is there supplementary bonding to the bathroom?
if the existing RCD is 30mA why would you want to fit another?
oops, misread OP. thing is, with a caravan, the site connection is usually on a 3omA RCD anyway. is this a static or a tourer?
No supplementary bonding which I have noted as C2. So I suppose that C2 would apply to absence of 30ma RCD protection too.
Maybe if the sockets are likely to supply equipment outside...I would say it's likely the case being a caravan. Then you also have to consider the installation method and what code it warrants.
Reply to Classification code for 100ma TT 3036 in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Need some advice, I have 7 static caravans to connect which need to be connected via TT 1. All the vans have a 30ma RCD main switch internally...
EICR installation 40 + years old… cabling PVC T&E… no MBPC… As stated fuses, all ELI measurements are ok… RCD separate from DB/CU 30ma, what’s...
Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and...
4K
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...