Discuss Coding question in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Pretty Mouth
Good morning all. How would you code the following?:
1 - Electric shower installed without RCD protection, where manufacturer states it is required? Supplementary bonding present.
Normally I would give this a C3, but in this case the manufacturer states RCD required, so am erring towards C2.
2 - No RCD protection for socket outlets in 3rd floor flat that could be used for mobile equipment outdoors.
The flat has a very large, uncovered balcony, so it is likely that outdoors mobile equipment would indeed be powered by sockets in the flat, potentially in a wet environment. For sockets in the ground floor of a building I would C2 this. However, this being a 3rd floor flat, I question if the level of danger is the same. I would imagine that someone standing on the balcony, receiving a shock, would not be at the same risk as someone standing on the ground receiving a shock. Could this be a C3?
Number 1 is a definite C2 from me.
Number 2 I could go either way, but would probably err on the side of caution and C2 it if the balcony is uncovered, susceptible to the elements and there’s evidence of use out there.
For the remedials, can you RCBO the circuits? Or looking at a board change?
EDIT
Just seen that sup bonding is present so could be argued that additional protection is present and therefore code as C3.
However, if there’s one place in a house where I’d want RCD protection, it’s when I’m taking a shower.
No. 1 - Definitely a C2 and agree with JBW175.... failing that a 61008 RCD mounted in a small enclosure next to the board with some cable jiggling to route the circuit through it.
No. 2 - I'm not sure of the conductivity of concrete but I suspect it's very low unless there is a substantial amount of moisture present. I may be inclined to do a bit of testing.... pour some water in patches at various places and then do an insulation resistance test between those patches and the MET (do a similar test on any metallic railings etc. that may be present). If you're getting high readings (in the order of Mega Ohms) I would probably C3 it. This time of year is a good time to check it as we've been having a lot of rain, which will have been watering the concrete quite well.
It's worth noting that pure water isn't particularly conductive, it's the minerals in it and this is where the concrete may become an issue.
The requirement for RCD for mobile equipment outdoors is generally based upon the user standing on the general mass of earth so could be argued that 3 floors up you are well insulated from earth but as per post #6 might be worth doing some testing so maybe a - FI?
You are inspecting to 18th edition which I believe (as dont have BBB to hand) calls for RCD protection to equipment in zone 1 and circuits serving the location, irrespective of supp bonding so C2 for me.
Thanks for all your replies. Normally I try to code according to best practice guide 4, but these instances don't quite fit the guidance.
Looks like it's a C2 for the shower then, which sits well with me. I don't like the idea of water and electricity coming together without RCD protection, particularly in bathrooms. Out of interest, would anyone have coded differently had the manufacturer not specified an RCD?
I think I'm going to give the sockets a C2 as well, erring on the side of caution.
The EICR is for a friend who rents her flat out, and while I don't want to create unnecessary work, I think a board change is probably necessary. The existing boards (on and off peak) are old proteus BS3871 boards, and I'm guessing current proteus RCBOs aren't going to fit. As @SparkyChick says, I could put RCDs in enclosures external to the board, but by the time I have done that I may as well have changed the board. The testing has already been done after all, which is the bulk of the work.
These are the consumer units. Can anyone confirm if current Proteus RCBOs will or will not fit them? I suspect not, the busbar is unlike any other I have seen. And not much space even if they do:
Reply to Coding question in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Hi all Called to do an EICR on a property 4 studio flats / bedsits within a single house. The t&e sub main to each flat runs within the fabric of...
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Hi all EICR today on a ground floor flat .. 1 issue .. At the consumer unit there was a 1mm core with its yellow (sleeved brown) in a 20A radial...
First : here are 2 x sockets .What code would you give and why ? 3rd pick you can see rear thermal damage on double socket second : Roof...
Hi, I have a property that I was looking to rent out. Its 12 years old property so relatively new. I had a EICR done from a qualified electrican...
7K