Discuss Consumer unit too close to gas meter in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
2
Good evening
Have to quote on a consumer unit replacement, problem is gas meter is next to existing consumer unit 25 mm between them, they are both in a wooden cupboard,
What would you do
 
Tricky one. Gas regs need 150 mm I think. Might be worth having a good read of the gas regs and seeing if a barrier of some description solves the problem.
Otherwise its an IP box, din rail, din terminal blocks and move the CU.
Or convince them to move the gas meter!
 
Maybe this will help:

BS6891-2005

8.16.2 Separation of installation pipework from other services

Where installation pipes are not separated by electrical insulating material, they shall be spaced as follows:

a) at least 150 mm away from electricity meters and associated excess current controls, electrical switches or sockets, distribution boards or consumer units;
b) at least 25mm away from electricity supply and distribution cables.
 
My reading of that is that if suitable “electrical insulating material” can be arranged there is no distance limit. I wonder what constitutes such a material. Presumably more than empty pvc trunking.

The only time I’ve had this issue it was not the only problem, trying to find a CU that fitted the space was hard with or without the gas pipe. I’m wondering if that applies to this situation too, e.g. if a rewireable wylex only just fits then fitting anything new in was next to impossible anyway.
 
Might be easier to insulate the gas piping. There are pvc sheaths that fit around 15mm & 22mm pipe; used cosmetically for radiator pipe drops. For main gas incoming idk maybe wrap some tape around it. Sometimes main gas piping is sleeved with yellow plastic; I guess this negates yhe 15mm away electricals rule !
 
Might be easier to insulate the gas piping. There are pvc sheaths that fit around 15mm & 22mm pipe; used cosmetically for radiator pipe drops. For main gas incoming idk maybe wrap some tape around it. Sometimes main gas piping is sleeved with yellow plastic; I guess this negates yhe 15mm away electricals rule !

Cant' imagine the decorative pipe sleeving will count as suitable insulating material far as the regs go!
 
Cant' imagine the decorative pipe sleeving will count as suitable insulating material far as the regs go!
The pipe sleeving is made of PVC, which is an 'electrical insulating material', so why not?
I'd consider dry plywood to be an 'electric insulating material' as well, so I'd be happy with a piece of 6mm plywood dividing the cupboard.
 
The pipe sleeving is made of PVC, which is an 'electrical insulating material', so why not?
I'd consider dry plywood to be an 'electric insulating material' as well, so I'd be happy with a piece of 6mm plywood dividing the cupboard.

The clip on pipe trim is made of material of an unspecified nature as far as electrical insulation goes. It's only purpose is to make copper rad pipes look acceptable. Must be barely a quarter of a mill thick also.
 

Reply to Consumer unit too close to gas meter in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi Guys Would I be correct in thinking an electric cable can be as close as 25mm to a gas meter ? (not that I'd ever be that close out of...
Replies
4
Views
789
I am planning to go semi off grid with a victron and battery system. The system will be installed in an out building about 20 meters away from...
Replies
7
Views
789
I live in a flat in Scotland supplied with an old 2 meter system called THTC where one meter using a time signal supplied heating and hot water...
Replies
7
Views
1K
Hi everyone, a landlord is converting a house into two flats and wants a separate consumer unit for both flats upstairs and downstairs. He also...
Replies
13
Views
1K
I have a large gym in the garden and it gets ridiculously hot in the summer. I have utilised pretty much every inch of space and do not want to...
Replies
23
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top