Hi guys, I have recently bought a Fluke 1652C and I am trying to work out how to carry out testing (course coming up soon) however I am a bit stuck with a continuity test I wanted to do on a ring circuit and would appreciate some help !

I was lucky enough to have an empty flat so carried out safe isolation, polarity of incoming feed, then ZE and PFC, however when I tried to do the continuity test in the consumer unit all the earths are connected on one main bar with no numbering on at all. There were about 20 earth connections and in the end I gave up !

Is there some magic way to work out which CPC's belong on which circuit ?

Thank you

Mike

PS All the wiring comes out of the wall behind the CU and it is impossible to see them !
 
if you can't physically see the cpc's coming out the T/E at the CU, all you can do is dis all the cpc's, bonding and main E, then link L and E at end of circuit, and ohm meter to find which is which. on RFCs, fins which cpc's are s/c to each other first. that will eliminate a few.
 
Thanks telectrix, I didn't think of joining the L & E together at the other end of the circuit, at least that way I can stay at the CU to carry out the OHMS testing. I guess I could use my "magic plug" as described by the Part P Doctor and put a link between L & E on that with one of my test leads from the Fluke. I suppose the other way would be to undo a socket and connect the L & E using may be a WAGO ? Unless I am missing an easier way ?
Thanks again Mike
 
you can use your breakout box and a link, but bear in mind that you will measure the R1+R2 + any resistance in the breakout and link. be sure to safely isolate and lock off the CU first, though.
 
Cool, back to the flat for more fun and games !
Thanks telectrix, all the best Mike
 
And dont forget you are trying to find 2 CPC's when you have disconnected them all and carrying out Tels method.

If you have the course planned, then this will be good experience for you. for some reason it is ring continuity testing that seems to get most people tied up in knots.

Once you have identified your conductors, try to test the ring as per GN3, and if you dont fully understand it , then shout up and ask, it is really easy once you know how.

Cheers.....................Howard
 
  • Like
Reactions: 1 person
Hi guys, I have recently bought a Fluke 1652C and I am trying to work out how to carry out testing (course coming up soon) however I am a bit stuck with a continuity test I wanted to do on a ring circuit and would appreciate some help !

I was lucky enough to have an empty flat so carried out safe isolation, polarity of incoming feed, then ZE and PFC, however when I tried to do the continuity test in the consumer unit all the earths are connected on one main bar with no numbering on at all. There were about 20 earth connections and in the end I gave up !

Is there some magic way to work out which CPC's belong on which circuit ?

Thank you

Mike

PS All the wiring comes out of the wall behind the CU and it is impossible to see them !
Three words: patience, logic & tenacity
 
  • Like
Reactions: 1 person
If I'm testing ring continuity for an EICR, I'll sometimes break the ring at a socket and test there. Then I only have two CPCs to deal with.
 
  • Like
Reactions: 3 people
Always good on those old 3036 boards where you cant work out what goes where and you dont want to start meddling incase something breaks!
 
  • Like
Reactions: 2 people
Always good on those old 3036 boards where you cant work out what goes where and you dont want to start meddling incase something breaks!

Or a stray wire makes its way over to the incoming line terminal which has lost its little push-on cover.
 
  • Like
Reactions: 1 person
Always good on those old 3036 boards where you cant work out what goes where and you dont want to start meddling incase something breaks!

This is exactly the thinking needed for the 2395 exam and periodic insp and test in real life. It says somewhere in GN3 that consideration must be given to unnecessary dismantling or words to that effect, just for the reason you mention.

Its worth remembering.

Cheers...........Howard
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Continuity Testing Help please !
Prefix
N/A
Forum
DIY Electrical Advice
Start date
Last reply date
Replies
12

Advert

Thread statistics

Created
MikeWindsor,
Last reply from
nickblake,
Replies
12
Views
2,265

Advert