I can't be bothered to read it all again so I'm sorry if I have forgotten or missed a bit.

Except for TNC-S the adiabatic is used to determine the csa of the earthing conductor.
This may work out to, say, 12mm but that means, of course, you would need to fit 16mm.

However, this would also mean that the bonding can be 6mm - half of 12, not half of 16.

It is not a straight question of what should I fit.

The question specifically relates to TN-C-S, and the situation when it is difficult to follow the regs.
 
The way forward with this should be.
1. Check the continuity and condition of the existing 6mm2 bonding. If there are no signs of corrosion or overheating at the connections and they are adequately labeled and soundly made you can proceed with the fuse board replacement.
2. Fit your fuse board ensuring you provide correct protection and board configuration.
3. Complete your EIC stating the following in the extent of works box. "Replacement of existing consumer unit with condition check and continuity verification of existing 6mm2 bonding for continued service"

With this you have explained what work you have completed and what steps you have taken to ensure the installation was of no safety concern on the day you completed the work. The regulations are NOT retrospective. On an EICR 6mm2 bonding on a TN-C-S system warrants a code C3 departure which does NOT suggest an unsafe condition. However if the sizing of the bonding is less than 6mm2 or evidence of deterioration is present this would require attention as a C2 departure would be justified as an unsafe condition.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

SJD

Mentor
Arms
~
Joined
Location
Braccan heal
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)
If other, please explain
Running own small electrical company.

Thread Information

Title
CU Change and Main Protective Bonding
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
22

Advert

Thread statistics

Created
SJD,
Last reply from
rattlehead85,
Replies
22
Views
4,025

Advert