I can't be bothered to read it all again so I'm sorry if I have forgotten or missed a bit.
Except for TNC-S the adiabatic is used to determine the csa of the earthing conductor.
This may work out to, say, 12mm but that means, of course, you would need to fit 16mm.
However, this would also mean that the bonding can be 6mm - half of 12, not half of 16.
It is not a straight question of what should I fit.
The question specifically relates to TN-C-S, and the situation when it is difficult to follow the regs.