currie123

Hi guys

What is the purpose of the third connection at a cylinder stat which appears to connect to the central heating pump on most wiring diagrams I have seen?

The system I have is what I assume to be gravity hot water with pumped central heating .

There are no motorised valves, just a pump switched on from the CH on terminal at the programmer, and the boiler switched on from the HW on terminal at programmer. I am to install a cylinder stat and I understand that it is just a switch to cut power to the boiler once temp rises, but not quite sure what purpose the number 2 connection has that appears to connect to the pump live?

When heating is selected at the programmer both the hot water and heating come on. Heating can be selected independently.

Thanks
 
C is the common, 1 is the N/O and 2 is the N/C. So C and 1 gives you a break on rise or 'ON' and C and 2 gives you a make on rise or 'OFF'

You can't just chop a cylinder stat in to a standard gravity system, the hot water channel fires the boiler and the heat gravitates to the cylinder with no temp control and then the heating channel and roomstat just operates the CH pump.
If you chop a cylinder stat in to the system then your heating will cut off once your hot water is up to temperature.

The common way to get a degree of temperature control over the hot water is to install a 2 port valve on the flow pipe to the cylinder and control this with a cylinder stat fed independently from the boiler system (usually fused from the I/H circuit as its the nearest supply).
 
Ok thanks.

So the cylinder stat would be positioned on the cylinder or on one of the pipes?

And could you explain how the cylinder stat and 2 port valve would be electrically connected?
 
Ok thanks.
So the cylinder stat would be positioned on the cylinder or on one of the pipes?

Seriously? the clue is in the name!


And could you explain how the cylinder stat and 2 port valve would be electrically connected?

Simply connect the cylinder stat so that the valve motor is energised when the temperature is below the set-point of the stat, you won't need the microswitch in this arrangement.

I'm surprised and electrician can't work that bit out for themselves
 

Reply to Cylinder stat in the Central Heating Systems area at ElectriciansForums.net

Similar Threads

I've always thought I was quite good a wiring heating systems, I can do Y plan, S plan, UFH set ups, "normal" thermal stores etc, you name it and...
Replies
4
Views
941
I have a fully pumped Y plan heating system using a Potterton EP2 programmer. Drayton MA1 Diverter valve. I have just replaced the Actuator head...
Replies
4
Views
615
I had to wire in an extra 2 port valve today to protect a newly installed unvented cylinder (replacing the old gravity fed one) in a standard Y...
Replies
12
Views
2K
Hello, I hope you are well, I have fitted a few Nests but only to Combi, S and Y plan systems just been looking a job where I’m doing the kitchen...
Replies
9
Views
2K
i , i have a property to work on which has a programmable room stat upstairs and a programmable roomstat downstairs. S plan system , 2 zones. hot...
Replies
5
Views
380

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock