Hello,
Last year I had a double socket (1) put in my room which was spurred off the ring main by a registered electrician.

This year, another company : -
i) installed two double sockets (2) and (3) either side of (1) and made the connection with flex wire
ii) left the blue and brown wires exposed under the new casing to (1) (he exposed the wires to the old cable that comes up through the floor )
iii) both flex cable was buried behind new skirting
iv) no certificate was left signed by reg'd electrician

I've deemed the work unacceptable but really want to learn where in the Regs it states it definitely is. Have had various electricians give their opinion but all very different and that's very worrying in deed. Still waiting for the certificate. Some say i) is ok with a cert, some say none of it ok. Thank you for your time reading this.
 
  • Dislike
Reactions: camerabloke
Think you'll need to post some pics, for your description to become apparent.

If they have spurred the additional sockets, off the original spurred socket with no additional local fusing (fused connection unit), then it would not comply with guidance from BS7671.
 
thanks for your response.
Where's does it say it isn't compliant to take two sockets off the existing socket?
is it ok to use flex?
should I have a certificate signed by registered person?

ive paid a 33% deposit
 
thanks for your response.
Where's does it say it isn't compliant to take two sockets off the existing socket?
BS7671 (The Wiring Regulations)
If the socket that he connected to is truly a SPUR from a RING FINAL circuit, and no other current limiting device is in play (eg a 13A FCU). Then this configuration is a spur from a spur is not permitted.
is it ok to use flex?
Yes, providing it is the same CSA as the other wiring in the circuit.
should I have a certificate signed by registered person?

ive paid a 33% deposit
All electrical works should carry an installation certificate.
In this case you should receive a Minor Works Certificate.
This can be done by the person who installs and tests the work. He/she does not need to be a registered electrician, but should be competent.
 
  • Agree
Reactions: Flanders
i) using flex is allowed.
ii) leaving the blue and brown cores exposed outside of an enclosure is not allowed.
iii) concealing the cable behind the skirting is not allowed.
The cable cen come up vertically through the floor, behind the skirting to a socket or switch, but the cable cannot drop down out of the socket to the skirting board, then run horizontally behind the skirting board and up vertically to the next socket.

The work is not complete until a certificate has been issued.
 
I would say from your discription that the job has not been done correctly , may be unsafe and would recommend you do not use these new sockets , Most electricians would not use flex to extend a socket circuit in a domestic environment , which is a red flag for me that the guy who did the work is not competent
 
  • Agree
Reactions: Dunc N and 123
How come you didn't use the first electrician to do the new works?
 
  • Like
Reactions: MDJ
BS7671 (The Wiring Regulations)
If the socket that he connected to is truly a SPUR from a RING FINAL circuit, and no other current limiting device is in play (eg a 13A FCU). Then this configuration is a spur from a spur is not permitted.

Yes, providing it is the same CSA as the other wiring in the circuit.

All electrical works should carry an installation certificate.
In this case you should receive a Minor Works Certificate.
This can be done by the person who installs and tests the work. He/she does not need to be a registered electrician, but should be competent.

It is if the spur is wired in 4mm.
 
Surely that depends on the OCPD, Volt drop, Zs is satisfactory etc

Some things are so obvious they are a given. It is not my fault if you are unable to keep up.

Please don’t take this the wrong way but you will probably benefit a lot from the trainee section. If you PM a Mod they can give you access.
 
If I recall correctly, spurs are limited to 20A max so the junction to the ring can't be "point overloaded". So 1 outlet or multiple after a fuse unit.
 
  • Like
Reactions: happysteve
i'll call your lollipop and raise you a candyfloss.
I reckon the next thing up would be a kebab? :)

So: "standard" lollipop circuit (6mm from the OCPD to a joint box, then standard RFC in 2.5mm), with one of Essex's 4mm spurs off that. ;)
 
  • Dislike
Reactions: 1 person
I can feel the love and joy overflowing in this thread..
 
  • Funny
Reactions: Midwest
Lollipop:
OCPD ----O

Inverse lollipop:
OCPD O----

Kebab:
OCPD ----O----

Maybe we can just carry on...?

????
OCPD ----O----O---- ...
:)
 
  • Funny
Reactions: Midwest

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Advert

Thread statistics

Created
hoitytoity,
Last reply from
Deleted member 26818,
Replies
28
Views
3,561

Advert