Advice please - suggestions/best practice.

Domestic property, TNCS supply, 25mm tails to RCBO C/U with 100A main switch.

I want to install a distribution circuit from the aforementioned C/U (I dont want to split tails) to supply a second RCBO C/U (essentially a garage board), serving little more than a lighting and power circuit.

The cable supplying the second board is 10mm T&E and already buried within the fabric of the building and will be used (non negotiable).

with discrimination in mind, what device should I be terminating the 10mm distribution cable, within the second board?

I am using Fusebox boards and the smallest main switch I can see is 63A. This is too big for the 10mm supply cable???

Any advice warmly recieved.

 Thanks
 
How did that user name get past the software filters?
If you’re trainee, as profile says, then @Dan can badge you as such


The 10mm cable is protected at the house end by a suitable sized rcbo….

The mainswitch at the garage is just a switch…. Not an overcurrent protection device.
 
How did that user name get past the software filters?
If you’re trainee, as profile says, then @Dan can badge you as such


The 10mm cable is protected at the house end by a suitable sized rcbo….

The mainswitch at the garage is just a switch…. Not an overcurrent protection device.
Blimey - that was painless (I anticipated an onslaught of responses).

Thanks Littlespark - appreciated.

Noted re the trainnee forum - I will move over there.

Download virus👍
 
This is the point of having a trainee badge... it allows you to ask simple questions without the critism reserved for have-a-go heroes.


Things to think about with the proposal though... You have a 10mm T&E existing... protected by rcbo... which it may have to be depending on how its run.
You would then not technically need rcbos on the outgoing circuits from the second CU, as the supply would be rcd protected anyway.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Earth
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Trainee Electrician

Thread Information

Title
Discrimination
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
5

Advert

Thread statistics

Created
Download Virus,
Last reply from
littlespark,
Replies
5
Views
490

Advert

Back
Top