Hi Everyone!
We build a 3 phase electric grill at my company.The grill has 6 elements.The elements are connected in delta, but..
4 elements work with a thermostat and 2 element work with an energy regulator.
So thermostat 4 elements connected:
L1-L2
L1-L3
L1-L2
L1-L3
Energy regulator 2 elements connected:
L2-L3
L3-L2
Also we have 3 led.Every phase have 1 led.
Phase 1 has the all 6 mini fan.
My problem is,i found 1 ampere on earth.If only energy regulator works with the 2 elements,no current flow to earth.Immediately i turn on the thermostat(4 elements) 1 ampere current flow to earth.
There is a 4 pole RCD what does not trip in this situation neither.
Neutral connected only to led and to fans.
There is no cross connection and the insulation resistances are all fine.
RCD disconnection time is fine and test button as well works.
My question is, how possible there is 1 amp on earth?
Why RCD does not trip?
Why i do not get electric shock if i touch the exposed metal part of the grill?

Thanks!!
 
Wi
How are you measuring this?

A diagrem might help explain how things are connected a bit better!
How are you measuring this?

A diagrem might help explain how things are connected a bit better!

With an earth clmap.
From main switch the 3 phase fo parrallel to the thermostat and to the energy regulator.
[automerge]1591039717[/automerge]
Wi

With an earth clmap.
From main switch the 3 phase fo parrallel to the thermostat and to the energy regulator.
Both can work separately.
 
You should measure earth leakage by clamping a suitable low reading meter around all live coductors, so 3 lines and neutral in this case, and taking a measurement.

This measures and imbalance and thus the total leakage from the circuit.
The actual leakage is often different to the current measured in a protective conductor.
 
You should measure earth leakage by clamping a suitable low reading meter around all live coductors, so 3 lines and neutral in this case, and taking a measurement.

This measures and imbalance and thus the total leakage from the circuit.
The actual leakage is often different to the current measured in a protective conductor.
Thank you very much!!
 
How big are these elements compared to your incoming supply. From your config, when the thermostat brings in the 4 elements its un-balanced and as such will create a neutral current. Typically L1 is a favourite phase anyway so you may have a very large neutral current caused by a large load on L1 compared to L2 or L3 at site level.Then it comes down to the type of earth system in place, i.e. TNCS where the N conductor is actually the earth. You may find that your grill has a better earth in the building than the return path of N back to the supply grid, hence you are seeing other Neutral currents coming your way.
Anyway i see large earth currents all the time in industrial and commercial settings. The RCD is monitoring the actual load so if its happy, then hopefully this will allay any fears.
You wont get a shock off the appliance but if you disconnect the earth and put yourself between the earth and the appliance you may well get a right old belt (dont try it)
 
How big are these elements compared to your incoming supply. From your config, when the thermostat brings in the 4 elements its un-balanced and as such will create a neutral current. Typically L1 is a favourite phase anyway so you may have a very large neutral current caused by a large load on L1 compared to L2 or L3 at site level.Then it comes down to the type of earth system in place, i.e. TNCS where the N conductor is actually the earth. You may find that your grill has a better earth in the building than the return path of N back to the supply grid, hence you are seeing other Neutral currents coming your way.
Anyway i see large earth currents all the time in industrial and commercial settings. The RCD is monitoring the actual load so if its happy, then hopefully this will allay any fears.
You wont get a shock off the appliance but if you disconnect the earth and put yourself between the earth and the appliance you may well get a right old belt (dont try it)
Thank you very much!
 
I have checked phases and neutral with earth clamp, but i have the same amount, 1 amp around.We built another grill but there is no current on the earth.Everything the same between these grills.Parts,elements,system etc..
 
Are you sure you are clamping all feed conductors? If it is an intermediate point you are measuring you might be missing one path (e.g. if live to control box is taken before and neutral returned after).
[automerge]1591080766[/automerge]
Also how does the "Energy regulator" you mentioned work? Is it some sort of high frequency switching regulator or similar? I'm wondering if there is some very unusual waveform that is upsetting your clamp meter.
 
Yeah,i was clamping all feed conductors at the main switch.
Is that the main switch of the equipment (i.e. internal) os part of some external test feed you are using?

If internal then can you repeat it on the actual feed cable where it is separate enough to clamp the phases+N but exclude the CPC?
 
Red in this case is neutral.I do not understand your question.So i share a picture.I clamped at both place(like on picture)
[automerge]1591102191[/automerge]
At first picture is 1 amp.at second more far from earth conductor is around 800 mA
 

Attachments

  • 20200602_134647.jpg
    93.6 KB · Views: 10
  • 20200602_134651.jpg
    59.2 KB · Views: 10

Reply to Earth current in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
Replies
19
Views
1K
Been called to help a friend who can't get anyone to look at his car lift until next week and it's stopping him from working. I said I'd have a...
Replies
14
Views
2K
Hi all, New to the forum. I have been asked to look at this for one of our guys who's had an issue onsite after some electrical works had been...
Replies
4
Views
728
Good morning, So I’m working on an existing 3 phase solar system and the customer wants a way to use the huge mass of exported solar on their...
Replies
3
Views
945
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
556

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock