Discuss Earth leakage circuit breaker in the UK Electrical Forum area at ElectriciansForums.net

goasis

-
Esteemed
Reaction score
400
From a brief bit of Internet research my understanding is earth leakage circuit breakers monitor voltage on the CPC rather than an inbalance in current between L &N as an RCD does. Is this correct?
 
While we are quizzing older and wiser people....
Was there a link between ceasing to be able to rely on water pipes as earth electrodes for TT systems and the introduction of VOELCBs?
I was quizzed the other day by a retired physics teacher on the history of TT systems before up-front RCDs and wasn't totally sure of which parts related to which other parts.
 
The VOELCB pre-dates plastic pipes by a long time!

For rural areas you might not have water mains supply, etc, anyway, it might be brought in by buckets, etc (I kid you not). Even if you did, it is not always going to be low enough to blow a 30A rewirable fuse for a cooker circuit!
 
The VOELCB pre-dates plastic pipes by a long time!

For rural areas you might not have water mains supply, etc, anyway, it might be brought in by buckets, etc (I kid you not). Even if you did, it is not always going to be low enough to blow a 30A rewirable fuse for a cooker circuit!
Thanks!
So was there ever an era when no up front device at all protected TT installations?
Or maybe (guessing) an era where earth electrode resistance had to be significantly lower that it needs to be today?
 
Thanks!
So was there ever an era when no up front device at all protected TT installations?
Or maybe (guessing) an era where earth electrode resistance had to be significantly lower that it needs to be today?
I am sure there was, but probably before the 1940s or so.

It is very hard to get a low enough earth impedance to blow even a 5A fuse, so by time the need for ADS was established then I think the VOELCB became the norm in rural areas where a 3rd conductor for E was impractical for cost or physical reasons.

@Lucien Nunes might know such details.
 
The VOELCB pre-dates plastic pipes by a long time!

For rural areas you might not have water mains supply, etc, anyway, it might be brought in by buckets, etc (I kid you not). Even if you did, it is not always going to be low enough to blow a 30A rewirable fuse for a cooker circuit!
You may be surprised or maybe not, a lot of French properties are still using well water, but now days pumped up to a header tank, no bucket required.
 
While we are quizzing older
Right, I qualify for this bit
and wiser people....
Not sure about this bit!
Was there a link between ceasing to be able to rely on water pipes as earth electrodes for TT systems and the introduction of VOELCBs?
I was quizzed the other day by a retired physics teacher on the history of TT systems before up-front RCDs and wasn't totally sure of which parts related to which other parts.
Correct. A TT system without sufficiently low RA to disconnect an OCPD requires an earth leakage device in order to function.
Did, nt get too many lessons on the history of earthing when I was serving my apprenticeship but my impression is that earthing as a concept only really got going from the 1950,s onwards. Up until that point electrical safety relied heavily on a "Don, t touch it" approach.
The only TT system I am aware of that has a sufficiently low RA to disconnect an OCPD (without using metallic service pipes) is to be found in mainland Europe
 
One issue with TT earthing in general is how dependant it is on the soil resistivity, and that is often down to moisture levels and so how deep you can go. To get, say, 0.4s disconnection reliably on the old 30A rewirable fuses you need something like 0.7 ohms for the rod (including whatever Earth impedance there is at the supply end).

Short of a buried steel foundation that is just not happening!

This article has some useful info and some handy plots. E.g. the buried horizontal conductor in 100 Ohm.m soil is not reaching 0.7 ohm even at 1km length!

 
This article has some useful info and some handy plots. E.g. the buried horizontal conductor in 100 Ohm.m soil is not reaching 0.7 ohm even at 1km length!

In practice the only countries that tend to use a low RA TT system are those with suitable soil conditions like the Netherlands. They can literally sink a copper wire vertically in to the ground without...
1)any obstructions in the way
2) permanently wet soil (sand)
 
Regarding the history...

Not all installations were always earthed. Although earthing and the TN supply concept was well established in principle by the 1920s there was not always a need for it. Many installations were either lighting only or for minimal use of appliances, many of which were class 0 and fitted with 2-pin plugs, so (especially with wooden casing and TRS installations) there was nothing that needed earthing.

All buried services were once metallic and of reliably low resistance, therefore any urban building with water laid on could get an amply low resistance earth. It was considered acceptable to use the water pipe as the main earth and no rod would be installed where a water pipe was available. In most pre-war domestic installations the largest circuit was 15A and indeed many had only 5A circuits on a 15A main supply or similar. Therefore no difficulty was encountered in clearing the fuse with an earth fault. Touch voltage and disconnection times were not the hot topics they are today; what mattered was that the fuse would blow.

Premises that did not have any earthed metallic services were significantly less likely to have a public electricity supply. Where present, there was the option of an installation that did not need earthing and/or had only low-rated circuits (as above, lighting points and 2-pin 5A sockets). Where electricity was generated on site, obviously the installation could be TN with the rod only needed as a potential reference. Electricity then being rarely used outdoors, a fault to real earth rather than CPC was less likely.

Obviously there were situations that needed a low Ra and didn't have one, but the impression I am trying to give was that these were not particularly common at first. Soon after the war, when increasing numbers of homes had a TN supply and more appliances, there was an increasing risk of the earthing being inadequate or missing. However, the ELCB was soon available as an option, so a properly executed installation was unlikely to be stuck without any acceptable solution. Improperly executed installations... well we still have those.
 

Reply to Earth leakage circuit breaker in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
Replies
19
Views
1K
Hello All, I am a homeowner (but not an electrician) and I am renovating a house that has an old CU containing MCBs and an MK LN5725 residual...
Replies
5
Views
807
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
346
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
780
Hi all, Just to be clear, I'm not looking for advice on upgrading but rather just clarification of our existing setup. We need to upgrade the...
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock