From a brief bit of Internet research my understanding is earth leakage circuit breakers monitor voltage on the CPC rather than an inbalance in current between L &N as an RCD does. Is this correct?
 
While we are quizzing older and wiser people....
Was there a link between ceasing to be able to rely on water pipes as earth electrodes for TT systems and the introduction of VOELCBs?
I was quizzed the other day by a retired physics teacher on the history of TT systems before up-front RCDs and wasn't totally sure of which parts related to which other parts.
 
The VOELCB pre-dates plastic pipes by a long time!

For rural areas you might not have water mains supply, etc, anyway, it might be brought in by buckets, etc (I kid you not). Even if you did, it is not always going to be low enough to blow a 30A rewirable fuse for a cooker circuit!
 
The VOELCB pre-dates plastic pipes by a long time!

For rural areas you might not have water mains supply, etc, anyway, it might be brought in by buckets, etc (I kid you not). Even if you did, it is not always going to be low enough to blow a 30A rewirable fuse for a cooker circuit!
Thanks!
So was there ever an era when no up front device at all protected TT installations?
Or maybe (guessing) an era where earth electrode resistance had to be significantly lower that it needs to be today?
 
Thanks!
So was there ever an era when no up front device at all protected TT installations?
Or maybe (guessing) an era where earth electrode resistance had to be significantly lower that it needs to be today?
I am sure there was, but probably before the 1940s or so.

It is very hard to get a low enough earth impedance to blow even a 5A fuse, so by time the need for ADS was established then I think the VOELCB became the norm in rural areas where a 3rd conductor for E was impractical for cost or physical reasons.

@Lucien Nunes might know such details.
 
The VOELCB pre-dates plastic pipes by a long time!

For rural areas you might not have water mains supply, etc, anyway, it might be brought in by buckets, etc (I kid you not). Even if you did, it is not always going to be low enough to blow a 30A rewirable fuse for a cooker circuit!
You may be surprised or maybe not, a lot of French properties are still using well water, but now days pumped up to a header tank, no bucket required.
 
While we are quizzing older
Right, I qualify for this bit
and wiser people....
Not sure about this bit!
Was there a link between ceasing to be able to rely on water pipes as earth electrodes for TT systems and the introduction of VOELCBs?
I was quizzed the other day by a retired physics teacher on the history of TT systems before up-front RCDs and wasn't totally sure of which parts related to which other parts.
Correct. A TT system without sufficiently low RA to disconnect an OCPD requires an earth leakage device in order to function.
Did, nt get too many lessons on the history of earthing when I was serving my apprenticeship but my impression is that earthing as a concept only really got going from the 1950,s onwards. Up until that point electrical safety relied heavily on a "Don, t touch it" approach.
The only TT system I am aware of that has a sufficiently low RA to disconnect an OCPD (without using metallic service pipes) is to be found in mainland Europe
 
One issue with TT earthing in general is how dependant it is on the soil resistivity, and that is often down to moisture levels and so how deep you can go. To get, say, 0.4s disconnection reliably on the old 30A rewirable fuses you need something like 0.7 ohms for the rod (including whatever Earth impedance there is at the supply end).

Short of a buried steel foundation that is just not happening!

This article has some useful info and some handy plots. E.g. the buried horizontal conductor in 100 Ohm.m soil is not reaching 0.7 ohm even at 1km length!

 