Discuss Earth Leakage? in the UK Electrical Forum area at ElectriciansForums.net

F

flukeyspark

Hi all,

Hope you can help..? Here goes... I split a kitchen/garage ring final and added 2 sockets, all end to end tests are fine, IR test >299 on megger so thats fine..The board is an old MK Sentry with 80A 30mA RCD as main switch. The circuit is fine until the washer is pulled in, then it trips, I've tried the washer on another circuit and again it trips...So im thinking its the washer? The customer says the washer never tripped the RCD before? I've tried to test the RCD but as soon as I plug my meter in it trips, same when trying to get a Zs reading. I've taken the kitchen/garage circuit off the board completely and still can not get a RCD or Zs reading due to tripping..So now im thinking its a dodgy RCD?
The customer has today called me to say a washing machine engineer has been out to look at the washer and told him its not either the washer or the RCD! He has told the customer he thinks its a problem with the circuit? As i said earlier all test for the circuit were fine... Anyone out there got any ideas? I've spoken to the NICEIC and they think is due to combined earth leakage and advised to put a meter on and test but doesn't a ramp test do the same thing?
Any help on this would be really appreciated

Thanks in advance
 
Sounds like a neutral to earth fault to me but this would be picked up by an insulation resistance test which you say has been done with good readings. Have you unplugged switched off everything on that RCD and tried an RCD test again?
 
Clamping with an earth leakage tester will give you an indication of what leakage there is. A Ramp test will tell you at what level of mA the RCD trips at, so they are different beasts
 
Sounds like a neutral to earth fault to me but this would be picked up by an insulation resistance test which you say has been done with good readings. Have you unplugged switched off everything on that RCD and tried an RCD test again?

Yeah insulation test at first found a fault on a garden pond pump, so took that off and then was spot on.. I can try to unplug everything but that may be difficult as the RCD is a main switch for the whole board/house. NIC said that maybe the IR test has mashed the RCD and is now tripping too soon? The RCD is an old MK one which they dont make anymore and the new ones wont fit the board.. :(
 
Clamping with an earth leakage tester will give you an indication of what leakage there is. A Ramp test will tell you at what level of mA the RCD trips at, so they are different beasts

Im going back armed with a earth leakage meter...Never used one before..Do I test each appliance or the CPC at the board?
 
Best way is to put the EL meter over the main earth, Turn off all other circuits and see what the offending circuit is leaking to earth with each appliance turned on in sequence. You can only put one on a earth, it wont measure a peice of flex with a LNE in it. A ramp test will only tell you how much fault the MFT has to introduce to trip the RCD, if there is already a fault present that will effect the reading
 
Best way is to put the EL meter over the main earth, Turn off all other circuits and see what the offending circuit is leaking to earth with each appliance turned on in sequence. You can only put one on a earth, it wont measure a peice of flex with a LNE in it. A ramp test will only tell you how much fault the MFT has to introduce to trip the RCD, if there is already a fault present that will effect the reading

Sorry i didn't explain properly, I have a small extension with the cpc cut out of the flex. So I plug my extension in the mains, the appliance in the extension and clamp the cpc in the extension? The problem is i don't know which is the offending circuit because when i plugged the washer into the dining room circuit it tripped the rcd...
 
By pass the RCD, as long as you remove bypass before it is returned to service you have no worries. A link in 2.5mm between L in and L out plus N in N out and you then can test it all to your hearts content. Before that ramp test the RCD at the board with all circuits off, that will give you an accurate indication of the RCD trip amperage. Below 17/18 mA and it needs replacing. 23-25 is ideal
 
By pass the RCD, as long as you remove bypass before it is returned to service you have no worries. A link in 2.5mm between L in and L out plus N in N out and you then can test it all to your hearts content. Before that ramp test the RCD at the board with all circuits off, that will give you an accurate indication of the RCD trip amperage. Below 17/18 mA and it needs replacing. 23-25 is ideal

May be solved..! I've just spoken to the washing machine guy, who incidently told the client that it was the circuit at fault, and I asked him what result he got when ramp testing the rcd...He said he got a reading of 19mA in the hall and 9mA in the kitchen. Faulty RCD? Only thing is why 2 different readings?
 
I guess a faulty RCD could give two different mA trip values but did you not say you we're unable do test the RCD because it trips every time you plug in your tester? Try swapping the RCD but it still sounds as if there is a neutral to earth fault somewhere. Have you disconnected all neutrals from CU then re terminate one circuit at a time to see if this narrows the fault down. I had a very similar fault which gave the exact same symptoms and turned out to be a damaged cable neutral to earth.
 
I guess a faulty RCD could give two different mA trip values but did you not say you we're unable do test the RCD because it trips every time you plug in your tester? Try swapping the RCD but it still sounds as if there is a neutral to earth fault somewhere. Have you disconnected all neutrals from CU then re terminate one circuit at a time to see if this narrows the fault down. I had a very similar fault which gave the exact same symptoms and turned out to be a damaged cable neutral to earth.

Yeah when i was there a couple of days ago I cannot get a result due to constant tripping and Im guessing the rcd had "warmed" up. The washing machine engineer is there today and he says he is now getting results...When you say a neutral to earth fault do you mean on the fix wiring to the property or on an appliance? How exactly do you mean disconnect all neutrals from the cu then re terminate? Sorry for being thick but fault finding isn't my forte..
 
I guess a faulty RCD could give two different mA trip values but did you not say you we're unable do test the RCD because it trips every time you plug in your tester? Try swapping the RCD but it still sounds as if there is a neutral to earth fault somewhere. Have you disconnected all neutrals from CU then re terminate one circuit at a time to see if this narrows the fault down. I had a very similar fault which gave the exact same symptoms and turned out to be a damaged cable neutral to earth.

and surely a N to E fault would show up on the IR test?
 
It could be either fixed wiring or an appliance, I would start by switching off and unplugging everything from all circuits and see if the RCD holds then that will rule out any neutral to earth faults on any appliances/extractors/heaters/showers etc. if you are now getting ramp test readings it would be worth swapping the RCD, quick and simple to do and rules out the RCD being at fault. Hope you get it sorted soon
 
think logical. assuming it was OK before you did your bit, then dis. the circuit yoiu have altered and then see if the fault has cleared. best way to use an earth leakage clamp meter is to clamp both L and E of the circuit together and the meter will then measure any difference. that will be the leakage.
 
think logical. assuming it was OK before you did your bit, then dis. the circuit yoiu have altered and then see if the fault has cleared. best way to use an earth leakage clamp meter is to clamp both L and E of the circuit together and the meter will then measure any difference. that will be the leakage.

I disconnected my circuit totally from the board and tried to get rcd results and Zs results but the rcd was tripping straight away... I'm going back next week with an earth leakage meter and try again.. Thank you.
 
I disconnected my circuit totally from the board and tried to get rcd results and Zs results but the rcd was tripping straight away... I'm going back next week with an earth leakage meter and try again.. Thank you.
So you've left them with a tripping rcd and unable to wash their clothes till next week?
 
So you've left them with a tripping rcd and unable to wash their clothes till next week?
No because they can have the washer working if the dishwasher isn't plugged in..but not at the same time... So everything on apart from washer, put washer in - trips. Everything on apart from dishwasher, plug dishwasher in and it trips.... This is why I'm think combined earth leakage is tripping faulty rcd? It's bizarre to be honest!
 
No because they can have the washer working if the dishwasher isn't plugged in..but not at the same time... So everything on apart from washer, put washer in - trips. Everything on apart from dishwasher, plug dishwasher in and it trips.... This is why I'm think combined earth leakage is tripping faulty rcd? It's bizarre to be honest!
Ah i see! It does look like a combined leakage, that rcd is tripping at an awful low value too, try replacing it
 
Ah i see! It does look like a combined leakage, that rcd is tripping at an awful low value too, try replacing it
If it is combined leakage how can this be solved as the main switch is the rcd. The reason im being so cautious is because this job is 150 miles away from me (go where the work is) so I need to go armed with everything and the kitchen sink!
MK LN 5780 80 AMP 30mA OLD STYLE RCD CIRCUIT BREAKER. | eBay This link is the rcd, as you can see its an old one....I need to get this right on the day so as much help as poss is very much appreiate.. Thanks again everyone! I'm still open to ideas by the way haha!!
 
If it is combined leakage how can this be solved as the main switch is the rcd. The reason im being so cautious is because this job is 150 miles away from me (go where the work is) so I need to go armed with everything and the kitchen sink!
MK LN 5780 80 AMP 30mA OLD STYLE RCD CIRCUIT BREAKER. | eBay This link is the rcd, as you can see its an old one....I need to get this right on the day so as much help as poss is very much appreiate.. Thanks again everyone! I'm still open to ideas by the way haha!!
First you need to find out what the leakage is, i would replace that rcd too because if it ramps at 19mA thats very low for a 30mA rcd, 24-27 is what you should be looking for. If it is higher than that you may have to split the circuit onto seperate rcd's or use high integrity earthing at socket outlets.
update: i know you should go where the work is but bloody hell! 150miles! I hope you're charging mileage!
 
well, for £4.95, i'd buy that RCD off ebay for starters. then find out where the local wholesalers are, so you can pick up any other bits required local to the job.
 
I disconnected my circuit totally from the board and tried to get rcd results and Zs results but the rcd was tripping straight away... I'm going back next week with an earth leakage meter and try again.. Thank you.

Here we go again, leave a disconnected circuit (that you have altered) over the weekend.

Do you have any sense of professional pride? Obviously not, the Friday night pint is so much more important, isn’t it?

You’re name will be mud within you’re customers circle of friends, bad news travels 50 times faster than good.
 
Here we go again, leave a disconnected circuit (that you have altered) over the weekend.

Do you have any sense of professional pride? Obviously not, the Friday night pint is so much more important, isn’t it?

You’re name will be mud within you’re customers circle of friends, bad news travels 50 times faster than good.

Tony, with respect, have you read this thread through its entirety? best that you do, then make a comment.
 
I’ve spent all my life in heavy industry.

It’s OK. We'll leave the plant shut down until Monday and I’ll sort it then.

I have never walked away from a job. I warned my (then future) wife, don’t think I will be back home at the end of every shift.
A 38 hour shift? I couldn’t/wouldn’t go home until things were running again.

OK I was paid well, but I was on a salary so didn’t get any extra. “It was expected!”

Sorry, but our ethics may be different.
 
I’ve spent all my life in heavy industry.

It’s OK. We'll leave the plant shut down until Monday and I’ll sort it then.

I have never walked away from a job. I warned my (then future) wife, don’t think I will be back home at the end of every shift.
A 38 hour shift? I couldn’t/wouldn’t go home until things were running again.

OK I was paid well, but I was on a salary so didn’t get any extra. “It was expected!”

Sorry, but our ethics may be different.

No Tony are ethics are not different, I want to sort this issue out, I am happy to travel 300 miles round trip to sort this out. Plus which the work I did has no fault and I advised the client to have his rcd checked. What's your advise on the issue please? Seeing as though, it seems your life was in electrics this should be a doddle.
 
Hi all,

Just wanted to let everyone that replied to my post that it is now solved! The problem was a faulty RCD. I got there this morning and ramped tested the RCD at the board with all the circuits switched off and got a reading of 15mA. I changed over the RCD, ramp test that and got 27mA :)
Got disconnection times of 28.8 x1 and 9.7 x5 and a Zs of 0.48. Obviously all appliances are staying on too, so customer can have washer and dishwasher running at the same time, all good!
Just a quick question - do you guys do a full installation test before you start any alterations? In hindsight this would probably spotted the problem before I started any work and I am now considering doing full testing before hand!
Thanks for your help on this subject everyone!

:)
 
This type of issues coming usually in the appliances so first switched off and also plugged off the appliances then do the RCD test it will show problem wherein appliances or earth leakage.
 
Last edited by a moderator:
Hi all,

Just wanted to let everyone that replied to my post that it is now solved! The problem was a faulty RCD. I got there this morning and ramped tested the RCD at the board with all the circuits switched off and got a reading of 15mA. I changed over the RCD, ramp test that and got 27mA :)
Got disconnection times of 28.8 x1 and 9.7 x5 and a Zs of 0.48. Obviously all appliances are staying on too, so customer can have washer and dishwasher running at the same time, all good!
Just a quick question - do you guys do a full installation test before you start any alterations? In hindsight this would probably spotted the problem before I started any work and I am now considering doing full testing before hand!
Thanks for your help on this subject everyone!

:)

So if everything was OK before you added these two extra sockets, then it was probably your IR testing that buggered the RCD then!!
By the way, the correct method of ''confirmation'' testing a RCD/RCBO is at the unit itself within the CU/DB, not downstream.
 

Reply to Earth Leakage? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
Replies
19
Views
2K
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
383
I sorted the fault fairly quickly as it happens but only because I'd come across it once before and at the time a few people said it couldn't...
Replies
13
Views
382
I've just picked one of these up on a famous auction site. The voltages, low and high resistance ranges all appear to be working fine but it's not...
Replies
7
Views
303
Hi, Just been scratching my head about this one and wonder if I've missed anything. A few weeks ago I installed a new circuit for a 3kw oven and...
Replies
6
Views
852

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock