I have a couple of old metal/brass lamps to which adding an earthed lampholder would be tricky (either the entry for 3 wires is VERY small or the lamp holder is integral to the lamp and is original). All of these lamps have a screw within the base which appear to be for an earth wire - is this a reasonably safe option? I've attached a photograph of one of my lamp bases for clarity.

In the photo you will see that the brown and blue wires are in the centre feeding up to the (not visible) lamp holder. The brown wire is not yet attached to the push switch at the centre top. on the right in the 4 o'clock position is what I believe to be the place for the earth wire. The entire lamp is brass with a sort of steel weight in the base and a metal shade (see picture 2). In this particular lamp, I might be able to squeeze a third wire in - but I have 2 others where this looks nigh on impossible - but they have the same set up.
 

Attachments

  • IMG_0223.JPG
    IMG_0223.JPG
    104.2 KB · Views: 192
  • IMG_7186.JPG
    IMG_7186.JPG
    89.6 KB · Views: 177
I have a couple of old metal/brass lamps to which adding an earthed lampholder would be tricky (either the entry for 3 wires is VERY small or the lamp holder is integral to the lamp and is original). All of these lamps have a screw within the base which appear to be for an earth wire - is this a reasonably safe option? I've attached a photograph of one of my lamp bases for clarity.

In the photo you will see that the brown and blue wires are in the centre feeding up to the (not visible) lamp holder. The brown wire is not yet attached to the push switch at the centre top. on the right in the 4 o'clock position is what I believe to be the place for the earth wire. The entire lamp is brass with a sort of steel weight in the base and a metal shade (see picture 2). In this particular lamp, I might be able to squeeze a third wire in - but I have 2 others where this looks nigh on impossible - but they have the same set up.
All I can say is yes that appears to be where you terminate your ground
 
You're not far off TBH, that's what I would use. Make sure you have a good mechanical connection between all metallic parts.

The OCD and ex-squaddie in me insists that the brass is polished to a very high standard!!!

?
 
  • Like
Reactions: DPG and Nightmer
As above, check that there is a solid metallic connection all the way to the lampholder, noting that the switch bush is as much in need of earthing as the lampholder. I hope there is a durable insulating cover over the base to prevent access to the switch terminals without the use of a tool - some lamps were sketchy on this point.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Earthing a vintage brass lamp to the lamp base
Prefix
UK 
Forum
UK Electrical Forum
Start date
Last reply date
Replies
3

Advert

Thread statistics

Created
Nightmer,
Last reply from
Lucien Nunes,
Replies
3
Views
4,394

Advert