Recent EICR from a NICEIC member at house being let out. I’ve visited today to quote for some minor works.
R1+R2 Every circuit “LIM”.
IR Every circuit “LIM”.
RCD times Every circuit N/A (despite all the sockets having RCD).
Earth fault loop impedance : Measurements !..but only Zs sockets, everything else “LIM”. House socket circuit and garage socket both exceed their minimum impedance in the schedule, but no comment or fault code.
RCD button Pass (well that was easy).
Circuit vulnerable to test: Every circuit “-“ .(Several in fact are vulnerable, such as fans to conservatory and wet rooms. I suppose it's irrelevant if they don't get tested)
Earthing conductor: Report reads 16mm. Unless I am very mistaken from quick visual, it’s 6mm, (Vernier calliper when I return). Adiabatic for this TNS gives minimum 6.6mm
Bonding conductor: Report reads 6mm but has “LIM” in all the optional fields (gas, water, structural steel etc). There is in fact.. no bonding to metal water and gas
Inspection schedule Reads “pass” in every field.
Overall conclusion : “satisfactory”.
R1+R2 Every circuit “LIM”.
IR Every circuit “LIM”.
RCD times Every circuit N/A (despite all the sockets having RCD).
Earth fault loop impedance : Measurements !..but only Zs sockets, everything else “LIM”. House socket circuit and garage socket both exceed their minimum impedance in the schedule, but no comment or fault code.
RCD button Pass (well that was easy).
Circuit vulnerable to test: Every circuit “-“ .(Several in fact are vulnerable, such as fans to conservatory and wet rooms. I suppose it's irrelevant if they don't get tested)
Earthing conductor: Report reads 16mm. Unless I am very mistaken from quick visual, it’s 6mm, (Vernier calliper when I return). Adiabatic for this TNS gives minimum 6.6mm
Bonding conductor: Report reads 6mm but has “LIM” in all the optional fields (gas, water, structural steel etc). There is in fact.. no bonding to metal water and gas
Inspection schedule Reads “pass” in every field.
Overall conclusion : “satisfactory”.