Discuss electric meter issue. The grid, meter or consumer unit issue? in the UK Electrical Forum area at ElectriciansForums.net

SC said 'loose connection' in the DNO's equipment in post #2 and I totally agree. A loose connection in the service cable joint for example. But others have gone on to be more specific by saying it's the neutral. Why? What evidence do we have that the neutral is faulty and not the line?

We've had a discussion with lots of good ideas about why high resistance connections are (thought to be) more common in neutrals, specifically in domestic installation work. Explanations include sparks habitually wiring the line first, then doing the neutral with waning concentration; or manufacturers using terminals of inferior design in CU neutral bars, etc. But does this apply to DNO equipment too, such as service cable joints? Where CNEs are terminated they have to be extra vigilant about continuity, so I'd almost expect a higher rate of failure in line connections.

Thoughts?

OP: I'd call the DNO. The problem is theirs, not yours, the meter display showing 'Low U' is a dead giveaway.
 
SC said 'loose connection' in the DNO's equipment in post #2 and I totally agree. A loose connection in the service cable joint for example. But others have gone on to be more specific by saying it's the neutral. Why? What evidence do we have that the neutral is faulty and not the line?

Have seen it happen a couple of times on my local estate alone, and both times I have spoken to the network guys and they confirm it is a common thing, mainly on joints from the 1970s. Didn't ask them their thoughts on why neutral, but wish I had now just out of interest!

Both times the symptoms were the same (flickering lights when other loads switched on, raised voltage on exposed metalwork, etc.).
 
100% is upstream of Meter as already said so it's the DNO issue to resolve. Could be line or neutral but frankly who cares at this stage......call the DNO and report it.

Awesome video OP :)
 
SC said 'loose connection' in the DNO's equipment in post #2 and I totally agree. A loose connection in the service cable joint for example. But others have gone on to be more specific by saying it's the neutral. Why? What evidence do we have that the neutral is faulty and not the line?

We've had a discussion with lots of good ideas about why high resistance connections are (thought to be) more common in neutrals, specifically in domestic installation work. Explanations include sparks habitually wiring the line first, then doing the neutral with waning concentration; or manufacturers using terminals of inferior design in CU neutral bars, etc. But does this apply to DNO equipment too, such as service cable joints? Where CNEs are terminated they have to be extra vigilant about continuity, so I'd almost expect a higher rate of failure in line connections.

Thoughts?

OP: I'd call the DNO. The problem is theirs, not yours, the meter display showing 'Low U' is a dead giveaway.

Not necessarily the joint in the cable where the neutral fails being more common.

However further back to the transformer sees quite often the star point connection failing, especially on smaller transformers.

Most DNOs as standard are fitting K Type transformers now with a 200% FLC rated star point connection.

These are failing due to the sharp increase of harmonics being put onto our distribution network.
 
Most DNOs as standard are fitting K Type transformers now with a 200% FLC rated star point connection.
Hi Rob! That's something beyond my area of expertise .... What is a "K Type transformer?" Or are you just saying it's a tx rated for a K factor of 2?
 
Hi Rob! That's something beyond my area of expertise .... What is a "K Type transformer?" Or are you just saying it's a tx rated for a K factor of 2?

A "K-Type" Transformer is a generic name used for a transformer that are designed to reduce the heating effects of harmonic currents. The K-factor rating is an index of the transformer's ability to withstand harmonic content while operating within the temperature limits of its insulating system.

The ones I have seen the DNO fit, and a few I have overseen installed, along with better quality insulation, offered a greater sized star point connection. (200% greater than the phases).

Because of the phase angle change by the transformer (most DNO transformers supplying LV have a DYn11 vector group). Harmonics can not pass through to the primary side. An thus the transformer needs to take the brunt of it.
 
Cheers, yeah I had a spike protection plug adapter on my combi- boiler plug and when the electricity supplier guy came to change the meter over (thinking that was the issue) he said it was probably the protector plug causing all problems and I should plug all appliances directly into mains. Then 20 minutes after he left the house flashed into disco mode, my plasma TV and boiler were going insane until i flicked off main power. So I hope no damaged has been caused :-(
 

Reply to electric meter issue. The grid, meter or consumer unit issue? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I am planning to go semi off grid with a victron and battery system. The system will be installed in an out building about 20 meters away from...
Replies
7
Views
726
Ok, most new Consumer unit seem to come with a 63A RCCB and two MCBs. Most house consumer units now will also have RCD of some type be it a dual...
Replies
24
Views
1K
I live in a flat in Scotland supplied with an old 2 meter system called THTC where one meter using a time signal supplied heating and hot water...
Replies
7
Views
1K
Hi all, what is the best way to configure surge protection in domestic dwellings when you have multiple consumer units? Does each consumer unit...
Replies
21
Views
4K
I want to know if my consumer unit (together with the digital meter) which is in a special metal container let into an outside wall near the...
Replies
2
Views
373

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock