Just a little thought here,

With PME / TN-C-S supplies being most common, and the difficulty with EV charging from this earthing arrangement are:

722.411.4.1:
(i) = Very difficult to ensure 3 phase loads are always balanced in the real world

(ii) = Unless in a new build with foundation electrodes or digging up a big garden and driveway and installing an earth mesh, very difficult to achieve an electrode with a low enough resistance, and with enough separation from any metalwork bonded to PME

(iii) = This would require an earth electrode even if its a small one, and then you still have PME separation issues

(iv) = This only works maybe 50% of the time and it is very possible to have an open circuit PEN conductor and the voltage to remain within the range, therefore not providing any protection, and giving a false sense of security

(v) = The only 2 devices I can think of like these are the Matt:e 3 phase o-pen which creates a simulated true earth point via the line conductors, this seems to be a good solution although not for domestic single phase installations. The other is the Zappi 2 charger which monitors the L - N voltage like in (iv) but it also has a current sensing coil around the CPC, so If there is a PEN fault and the voltage remains within the acceptable range if any current is flowing on the CPC (by contact of EV metalwork and true earth) then it will disconnect, the issue I see with the zappi is the current sensing part is not automatic disconnection and requires user intervention (in the case of a person in contact with the EV and true earth, to receive a shock for a very short duration to achieve disconnection)


Last option = Make the EV charge TT, which in some locations can be very hard to achieve due to buried metal work bonded to PME, such as water and gas pipes, and PME cable joints with electrodes. Also if the car charger is located close to anything else such as an outside light bonded to the PME earth there is a touch voltage risk between the EV and the outside light, etc


My thought is surely all of these problems could be avoided by having the charging & related circuitry in the EV double insulated, and therefore the exposed metalwork of the EV would not need to be bonded. Then a PME earth could be used as there is no risk of contact with PME earth and true earth in the event of a PEN failure


I understand EVs might use the chassis as there negative under normal running conditions, but maybe when on charge this could be isolated. Of course this is just a thought and would be a big ask to tell every manufacture to double insulate there charging electronics!! The only way it would happen is if a law was passed to require it.


What are your thoughts on this, I am not looking for answers just interesting to think it through.



Thanks Marcus
 

Reply to EV & TNCS Food for Thought in the Electrical Engineering Chat area at ElectriciansForums.net

Similar Threads

Hi all, Merry Christmas to everyone, and apologies for talking work during the holidays😅 I have my first EV charger install job early in the New...
Replies
14
Views
2K
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
676
I'm going to start some construction projects at my own gaff soon, including sorting out some better outdoor supplies. Currently have a 32a...
Replies
7
Views
1K
Hi, I’m after some advice for an existing car charger that’s on one of our newly inherited sites. We have a Rolec 2x 7.2kw pedestal charger, just...
Replies
0
Views
1K
Hello everyone, I’m based in the ROI and live in a rural location. Yesterday evening my electricity supply started to switch on and off randomly...
Replies
2
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock