For an UNFUSED spur there is a limit of only one point. Which, if a double socket, is maximum 26A if both outlets are used with a 13A plug.

Very unlikely that would happen, so we assume a max 20A load on that spur…. And 2.5mm cable can easily take 20A.

We use 32A on a 2.5 ring, because it IS a ring.
Any point is supplied by 2 x 2.5 cables…. Not just one.
 
For an UNFUSED spur there is a limit of only one point. Which, if a double socket, is maximum 26A if both outlets are used with a 13A plug.

Very unlikely that would happen, so we assume a max 20A load on that spur…. And 2.5mm cable can easily take 20A.

We use 32A on a 2.5 ring, because it IS a ring.
Any point is supplied by 2 x 2.5 cables…. Not just one.
Thankyou littlespark, then my question is, if we can use 2x2.5mm T+E to create a ring on a 32A breaker. If I add a spur from a junction box or socket outlet, is there a calculation or any evidence in BS7671 to explain why this cable 2.5mm spur isn’t at risk of overheating ? I don’t understand the scientific/ numerical aspect behind this.
 
2.5mm rated @ 27 amps I do believe… you are allowed 1 Twin socket on a spur .. thus max overload current would be 26 amps @ that point
32 amp RCBO/MCB protects the actual RM from short circuit, the fuse in the plug top provides overload protection
 
It’s the fact that an unfused spur can ONLY take a maximum of two things plugged into a double socket limits how much current can actually run through the spur. 2 x 13A = 26.

That is why we don’t allow more than one point on an unfused spur. Then it could overheat with maybe 3 x 13 running through it.


The joys of fused plugs.
 
Thankyou littlespark, then my question is, if we can use 2x2.5mm T+E to create a ring on a 32A breaker. If I add a spur from a junction box or socket outlet, is there a calculation or any evidence in BS7671 to explain why this cable 2.5mm spur isn’t at risk of overheating ? I don’t understand the scientific/ numerical aspect behind this.
433.3.1 (ii) applies in the case of a spur from a ring.

As @littlespark mentioned, a double socket is only expected to take a maximum continuous load of 20A (I believe that BS1363 only requires a twin socket to take a 20A load). This does not exceed the cable rating required from a ring final by 433.1.204
 
I’m pleased 443.1.204 was mentioned!

It’s very common for the informative appendix to quoted as de facto regulations when in fact it’s simply an easy/common way to make sure 433.1.204 is complied with.

The key concept in the reg itself is expectation of likely use in terms of load and duration.
I’ve run more that one double socket on an unfused spur in a data cupboard where all six sockets had plug in transformers.
I don’t recommend doing this at the drop of a hat but it isn’t a banned practise as the cumulative expected load is (significantly) under 20amps.

I have no doubt that one day someone will insist a fused spur is inserted as it seems not many electricians read the actual reg about RFC’s, just the appendix.
 
Go on then, what's regulation 443.1.204 ?

Or do you want to correct the typo?

:)
443.1.204 : Early in the morning when spotting a mild hangover, phones shall not be used to type anything requiring any level of detail.
(Can’t correct now, too late!)
 
2.5mm rated @ 27 amps I do believe… you are allowed 1 Twin socket on a spur .. thus max overload current would be 26 amps @ that point
32 amp RCBO/MCB protects the actual RM from short circuit, the fuse in the plug top provides overload protection
Thanks everyone, my question that that cliffed is: If in the event of a fault is there not a risk that the single leg 2.5mm spur to a double socket could become damaged ? If the MCB is rated to 32 Amps and the cable rated to 27 amps ? Thankyou 👍🏽
 
Thanks everyone, my question that that cliffed is: If in the event of a fault is there not a risk that the single leg 2.5mm spur to a double socket could become damaged ?
Yes...but over a very long time.

If you go from 27A to 32A then the heating is increased by (32/27)^2 = 1.4 so your temperature rise goes up by roughly 40%, and from the usual assumption of 20C->70C defining the CCC then your 40% increase is taking the wire to 90C. Above its ratings for sure, but very far short of bursting in to flames.

The 20C excess temperature will typically increase the cable ageing by a factor of 2-3 depending on the type of reaction that degrades it, so the nominal 25+ year lifetime is now down to 10-ish years.

Assuming you run at full load all the time, and with 32A being about 7.3kW that would be around £1.5k per month. Which is a touch more than most folks can afford!
 
Thanks everyone, my question that that cliffed is: If in the event of a fault is there not a risk that the single leg 2.5mm spur to a double socket could become damaged ? If the MCB is rated to 32 Amps and the cable rated to 27 amps ? Thankyou 👍🏽
Take it up with the IEE.....but they won't explain it any better than you've seen already.
 

Reply to explanation of using 2.5mm2 T+E for a spur from a ring 32A (ring) in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi guys, newbie posting! Does the following sound ok... Existing circuit: SOCKET on a ring -> spur to SWITCHED 3A FCU -> SWITCH -> hardwired FAN...
Replies
11
Views
664
Ok. Can you cut a ring in half, add junction box, then run a spur off it? I thought it had to be from a socket? Mate of mine wanted me to see if...
Replies
3
Views
753
Grateful if someone could offer some advise, I'm struggling to find a definitive answer to this. I have a double socket, it was on the ring main...
Replies
8
Views
649
Hi, looking for some advice on what I have seen at my mums house when I took the cover off the consumer unit. 32A breaker, labelled kitchen...
Replies
17
Views
2K
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
464

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock