I know this is going to cause madness but how would this work exporting the earth is driving me nuts i feel like its a hard one to understand

for example a house has a tncs and it supplies a metal shed that is a TT system so the earth has not been exported.

the shed is 30m from the house

the house has a metal fence that runs from the house to the shed a class one light is on the fence at the house end supplied by the tncs

and at the shed end a light is also connected but supplied by the TT system

would that not link the two types of earthing systems?
 

Attachments

  • 20210105_214058.jpg
    256.7 KB · Views: 19
easy solution. isolate the light at the shed end from the fence , using non-conductive fixings.
 
If you have continuous metal between the 2 lights, then the 2 earthing systems will indeed be connected. Class II fittings, or keep both lights on the same earthing system, perhaps supplied from the shed end.
 
It depends, just because the luminares are class 1 it doesn't necessarily mean that contact of the earth/cpc with the fence is made.

Many fittings have insulated housings, whilst the main part is metal and connected to cpc.

You need to either physically check, or measure.

The one of great concern is the one connecting the fence to the house cpc, if it is connected, it in effect is bonding the met to an extraneous conductive part, which typically needs to be 10mm^2, not 1.5mm^2 or whatever it is currently.

This is assuming the fence goes into the ground, if it's isolated from ground then the cpc size is not so important
 
Last edited:
This is assuming the fence goes into the ground,

jusrt trying to visualise a metal fence not going into the ground but hovering above it visions of Dynamo the magician.
 
or plastic fence posts. beats the corrosion issue.
 
Hi - as per @Julie. ... at the house end do whatever is required (change the light fitting?) so that house CPC does not get connected to the metal fence.
 
I know this is going to cause madness
Getting used to "madness" is unfortunately a requirement for electricians. The situation you describe is a perfect example. Many electricians on this forum can remember a, time when we did, nt did, nt have to cope with the type of problem you describe. However, cost won out over quality of service and so TNC-S was born. We are where we are.
Previous posts have mentioned some practical solutions. One other possibility is to put the fence light on with the shed supply and have it operated by a sensor.
 
It depends, just because the luminares are class 1 it doesn't necessarily mean that contact of the earth/cpc with the fence is made.

Many fittings have insulated housings, whilst the main part is metal and connected to cpc.

You need to either physically check, or measure.

The one of great concern is the one connecting the fence to the house cpc, if it is connected, it in effect is bonding the met to an extraneous conductive part, which typically needs to be 10mm^2, not 1.5mm^2 or whatever it is currently.

This is assuming the fence goes into the ground, if it's isolated from ground then the cpc size is not so important
Even if it is connected to ground its worth measuring whether it has a high or low resistance to ground. An extraneous part with a high resistance won't require a 10mm strictly speaking as it can't import any currents that would have damaging thermal effects
 

Reply to Exporting an earth xD in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Curious one and hopefully some one of you could give me some advice. A customer has had a steeltech shed installed at their premises. A...
Replies
17
Views
1K
Hi all, New to the forum. I have been asked to look at this for one of our guys who's had an issue onsite after some electrical works had been...
Replies
4
Views
788
Fitted a remote second consumer unit to a detached annex. The supply to it was from a tncs system. The new db has been changed to a tt system for...
Replies
1
Views
790
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Replies
18
Views
2K
As the title says, I am looking for a recommendation for an enclosure and gland arrangement to electrically isolate or divorce the earth/armouring...
Replies
25
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock