Hi just looking for some advice,
Extension has been built onto the side of a
house and they are putting in a separate consumer unit (just for the extension) and it will be fed off the existing consumer unit with a 16mm T&E. Distance between the 2 boards approx 6 metres. It’s a big enough extension so that’s why they would like their own board.
The existing board mains fuse is 63A.
Would you recommend my new tails feeding the new CU be terminated in with the incoming supply (meter supply into the existing CU ) or come of the load side of the fuse in the existing CU?
Or any other options?
Thanks in advance
 
, split tails with henley blocks and fit a 63A switched fuse to feed DB2.
 
I'd suggest taking the 16mm from an additional device in the existing CU would be a very poor design as there's a chance of overloading. You need to split the tails after the meter using 100 amp single pole blocks and connect a 63amp metalclad switch fuse for your new 16mm to the extension CU. But there's another consideration as the sub-main may well need additional 30ma RCD protection depending on how it's been installed and the route.
 
I'd suggest taking the 16mm from an additional device in the existing CU would be a very poor design as there's a chance of overloading. You need to split the tails after the meter using 100 amp single pole blocks and connect a 63amp metalclad switch fuse for your new 16mm to the extension CU. But there's another consideration as the sub-main may well need additional 30ma RCD protection depending on how it's been installed and the route.
last bit.... he could use SWA, to eliminate RCD.
 
Feeding the 2nd CU from the first CU would mean it is off a MCB (possibly also RCD protected) and likely to have poor selectivity with the protection in the 2nd CU itself.

Feeding it from a switched-fuse off the (split) incoming tails would give the best selectivity, but the remaining question would be if the T&E needs RCD protection. I have no idea under what conditions the ROI regs demand it, but assuming they are broadly comparable to our 18th then either the T&E needs physical protection and/or careful routing to be > 50mm deep in any walls, etc.

Or go for the the safer and more professional option is to use some SWA with proper glands to terminate the armour at the switch-fuse and at the 2nd CU and not require RCD protection (assuming TN, and not a TT supply, of course, that is a whole other can of worms).

Even if going down the T&E route you should really be using some matching glands for cable entry protection and physical support such as these:
 

Reply to Extension supply in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Customer has an extension and this compromises existing meter position, DNO is extending incomer and putting meter box on a different...
Replies
3
Views
403
Been asked to move, remove and add some sockets the kitchen and I’ll need to add a circuit for an electric hob. Looked at the board and it’s one...
Replies
17
Views
695
Some advise or views would be appreciated. My supply is 100 amp single phase. I purchased my property 3 years ago or so, the owner prior to the...
Replies
29
Views
854
Morning guys! Went to look at a consumer unit change today with a PME supply. Now, right next to this was an old BS3036 60A fused mem cutout...
Replies
2
Views
696
Afternoon all. I’m doing a dorma / loft extension all circuits for that extension are new . I’m going to upgrade the consumer unit also to...
Replies
1
Views
947

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock