Discuss Fire Alarm Segregation. in the Security Alarms, Door Entry and CCTV (Public) area at ElectriciansForums.net
S
shaun gold
I'm having an on going argument with fire alarm engineers that run the 230 volt supply for the panel along with the fire alarm circuit installation (more often than not, clipped together in the same trunking). Both are in FP 200 cables but should they be
separated as you would normally. Does the fact they are both insulated to the same rating make it ok or would there be
Interference to the fire alarm circuit pulses by possible EMF.
should not be a problem as the cables, as you say, are rated for the same voltage. can't see an interference problem either.
only problem i can see is that if there are a bunch of FP cables together, some plonker may think they're only 24V and wreck his new snips. tough.
Sorry to disagree with you both!
The BGB clearly states that cabels of safety circuits should be segregated from normal circuits. with a minimum distance between them.
But I stand to be corrected if im wrong.
maybe so, but the 230V supply cable to the alarm panel is, itself, a part of the safety system.
Yep I guess so telectrix.
All the alarms that I have wired or been involved in are segregated. When doing testing or commisioning have always made a note on the certificate if they aren't.
If the insulation rating meet the same of all cables then there is no problem...but commercial installs set a good practice of usually seperate 50mm basket/tray for ultra low voltage cabling ie data, security and fire alarms and 150mm + for 230-410v. It makes life easier for on the install all round
Reply to Fire Alarm Segregation. in the Security Alarms, Door Entry and CCTV (Public) area at ElectriciansForums.net
Good evening! Don’t have a huge deal of experience with fire alarms but having to work on a conventional system at the minute with various...
Hi, I need to extend a fire alarm, the panel is a CTEC CFP 2 zone one and currently it has a couple of apollo alarm sense sounder bases/heads on...
4K
On this commercial building we are refurbishing it has the above fire alarm panel which I think is pretty much brand new, I'm not even sure it was...
Hello People Our Enphase solar system needs to have the AC supply shut down via the fire alarm contactors local input output unit that has NO &...
Not wanting to derail the Dodgy work pictures thread but a comment was made that a fire alarm FP200 shouldn't be in trunking with 230V band 2...