I have a Fluke 1653 multi function tester and after testing on a TT system need help to ensure I am recording the correct readings from the display.

Readings are as follows :-

Main earth disconnected, Z1 (loop) selected, F1 L-PE selected and three leads connected. Green to main earth, blue to in neutral and red to in line. Test = upper display 0.40 ohms, lower display 619A. F1 L-N selected, Test = upper display 76.3 ohms, Lower display 3A.

Main earth connected, Z1 (loop) selected, F1 L-N selected, Test = upper display 26.6 ohms, lower display 9A.

Am I correct in recording Ze as 0.40 ohms, PFC as 619A and earth electrode resistance as 76.3 ohms

Are these readings acceptable and If not – where am I going wrong?

A quick reply with assistance would be appreciated as I cannot put the installation live until 100% and need to certify asap.

Thanks
 
Ah, the joys of using a three lead instrument with too many function buttons... Give me a nice Megger two lead set, then you know for sure which loop you're reading as it will be whichever one your probes are on!

In reply though, loop reading for a TT will be higher than 0.40, so could be the 70 or 20 odd reading you have. But it seems strange that you got the low reading on what appears to be the correct setting. Not having used Fluke MFTs too much then that's all I can say, but there are many Fluke users on here that will be able to help you, :)
 
Re: Ze, EARTH ROD RESISTANCE AND PFC TEST ON TT SYSTEM

I have a Fluke 1653 multi function tester and after testing on a TT system need help to ensure I am recording the correct readings from the display.

Readings are as follows :-

Main earth disconnected, Z1 (loop) selected, F1 L-PE selected and three leads connected. Green to main earth, blue to in neutral and red to in line. Test = upper display 0.40 ohms, lower display 619A. F1 L-N selected, Test = upper display 76.3 ohms, Lower display 3A.
I'm not familiar with the tester but your results appear the wrong way round...if the main earth is going straight to the electrode on the first test I would expect the second set of readings and for the L-N test (second test ) the first set of readings.
So the Ze and ELR would be 76.3 and the PFC 619a.


Main earth connected, Z1 (loop) selected, F1 L-N selected, Test = upper display 26.6 ohms, lower display 9A.

Am I correct in recording Ze as 0.40 ohms, PFC as 619A and earth electrode resistance as 76.3 ohms

Are these readings acceptable and If not – where am I going wrong?

A quick reply with assistance would be appreciated as I cannot put the installation live until 100% and need to certify asap.

Thanks

hope this helps
 
Last edited by a moderator:
I don't know much about the fluke testers, but I'm pretty confident you won't have anything like as low as .40 on a TT. Using a loop tester to measure earth electrode resistance, your Ze and electrode resistance will be more or less the same and will probably be the higher 76 ohm reading.
76 is normally acceptable for electrode resistance and Ze but you should prove this yourself by referring to the regs.
 
I don't know much about the fluke testers, but I'm pretty confident you won't have anything like as low as .40 on a TT. Using a loop tester to measure earth electrode resistance, your Ze and electrode resistance will be more or less the same and will probably be the higher 76 ohm reading.
76 is normally acceptable for electrode resistance and Ze but you should prove this yourself by referring to the regs.


Just to refer back to your comments. I retested and got between 76 and 77 ohms for RE on earth electrode but stil got between 35 and 40 for Ze ??
 

Reply to Fluke testing on tt system - urgent assistance please in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...
Replies
5
Views
1K
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K
Hope this all makes as much sense as i can make of it and my "problem" can get sorted via some guru on here... Just a quick background on myself...
Replies
4
Views
962
Hi, I would love some help understanding an issue I’m having on a 16mm SWA cable running from the CU in my house to the CU in the shed. I believe...
Replies
15
Views
2K
Over the last few days, I have stumbled across a number of threads that seem to point to a prevalent misunderstanding. Either that, or I have been...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock