Evening gents, just seeking a little advice. Recently bought a new place, it has mostly been rewired, its on a TN-CS system. The garage which is approx a 40m run from the house is supplied by a 2.5mm cable believe it or not, it is donkeys years old. This supplies a 2 way rcd board in the garage, the wiring in the garage is all new T&E, which supplies a few lights and socket outlet.

Going to run a new 10mm SWA 3core armoured from the board, some of which will be clipped to a fence and some burried. Going to put this on a 40amp RCBO. With regards to the earthing arrangement in the garage, would it be sufficient to use the earth from the MET, or do you think it would be better to have it off an earth rod. Just thinking distance wise, might be better off with the second option. Thanks in advance. I am a qualified electrician, just have a been out the game for a couple of years.
 
  • Optimistic
Reactions: DPG
I wouldn't be clipping a cable to a fence - its not a permenant structure.

And surely you know its not good practice to have 2 RCD's in series

And why 40A - are you turning it into a habitable space?
 
It's not ideal to have 2 MCB's in series either
 
  • Agree
Reactions: Risteard
and why 10mm if you only want 40A? surely if you're going to the expense of 10mm, bung it on a 63A.and use the PME. your 10mm cpc is adequate for bonding. fuse at supply end. then MCBs at garage.
 
  • Like
Reactions: SparkyChick and DPG
A fence is a fixed structure, it's new, concrete posts, concrete gravel boards, it won't be coming down very easily or anytime soon. Not converting the garage into a room, however I am sizing up for the length of the run 40m), volt drop etc and anything to be added to the garage down the line. I am aware that you don't have to have an SWA on rcd protection, I just prefer prefer to protect the armoured running to the garage.
 
and why 10mm if you only want 40A? surely if you're going to the expense of 10mm, bung it on a 63A.and use the PME. your 10mm cpc is adequate for bonding. fuse at supply end. then MCBs at garage.

Thanks telectrix, sounds like a good solution, 63a rcbo at the supply of the swa, switch the rcd in the garage board with a main fuse.
 
  • Disagree
Reactions: DPG
and why 10mm if you only want 40A? surely if you're going to the expense of 10mm, bung it on a 63A.and use the PME. your 10mm cpc is adequate for bonding. fuse at supply end. then MCBs at garage.

10mm volt drop = 4.4mV/A/m. At 40m run, assuming there are lights in the garage (so 3% i.e. 6.9V max) then:

max Ib = (6.9 x 1000) / (4.4 x 40) = 39.2A

(not allowing for the volt drop contribution of (R1+Rn) and Ib of the lighting circuit in the garage, though likely to be small).
 
  • Like
Reactions: cairns1990
10mm volt drop = 4.4mV/A/m. At 40m run, assuming there are lights in the garage (so 3% i.e. 6.9V max) then:

max Ib = (6.9 x 1000) / (4.4 x 40) = 39.2A

(not allowing for the volt drop contribution of (R1+Rn) and Ib of the lighting circuit in the garage, though likely to be small).
Yeah 40amp rcbo then, thought initially 40amp. Cheers for your input, you've all been really helpful
 
  • Disagree
Reactions: DPG
Thanks telectrix, sounds like a good solution, 63a rcbo at the supply of the swa, switch the rcd in the garage board with a main fuse.
NO. 63A fuse at supply end. RCD protection and MCBs in garage.
 
  • Like
Reactions: DPG and cairns1990
A fence is not a permanent structure in the eyes of insurance companies.

A fence is a fixed structure, it's new, concrete posts, concrete gravel boards, it won't be coming down very easily or anytime soon. Not converting the garage into a room, however I am sizing up for the length of the run 40m), volt drop etc and anything to be added to the garage down the line. I am aware that you don't have to have an SWA on rcd protection, I just prefer prefer to protect the armoured running to the garage.
 
A fence is not a permanent structure in the eyes of insurance companies.
Nor is a shed (usually). I'm wondering, when wiring up a shed, would you recommend we use skyhooks or witchcraft as a method of support for the wiring system? I've looked in OSG Appendix D, and can find no reference to either.
 
Only use skyhooks for temporary lighting.
Well, the shed lighting will be temporary as it's a temporary structure, so good advice, skyhooks for the lighting circuit then. Witchcraft for the sockets?
 
I don’t even think you can get a 63amp rcbo btw
Don't recall ever using or seeing one, but you can get them for sure like here.

I'd be surprised if Hager and other big manufacturers don't do them, although they would charge handsomely for them no doubt
 
I don’t even think you can get a 63amp rcbo btw
Toolstation sell a Protek 63 amp RCBO for around 25 quid.
Its a type B where as most of the 63 amp ones i have seen have been type c.
 
No, it’s not. This post is however about a permanent structure.

Although what the op proposes is a bodge no matter what.

Nor is a shed (usually). I'm wondering, when wiring up a shed, would you recommend we use skyhooks or witchcraft as a method of support for the wiring system? I've looked in OSG Appendix D, and can find no reference to either.
 
SHHHH. cannabis farm in shed.
 
But WHY such a high design load ?
At 40m...Electric Heating, Electric Water Heater. Saniflow. Lighting. Sockets. Electric Roller Door
 
  • Funny
Reactions: 1 person
Well, the shed lighting will be temporary as it's a temporary structure, so good advice, skyhooks for the lighting circuit then. Witchcraft for the sockets?

Good sparks can be hard enough to source...but a competent witch,once found,should be treasured.

Hats are good for splaying cores,working live...just throwing it out there...
 
A fence is a fixed structure, it's new, concrete posts, concrete gravel boards, it won't be coming down very easily or anytime soon. Not converting the garage into a room, however I am sizing up for the length of the run 40m), volt drop etc and anything to be added to the garage down the line. I am aware that you don't have to have an SWA on rcd protection, I just prefer prefer to protect the armoured running to the garage.
A fence might be a fixed structure but its not a permanent one. Get the shovel out and bury the cable in a duct.

Why isn't an armoured cable protected by an MCB? Why do you need it on an RCBO?
 
Just had a proper measure it's 55m run. In terms of digging a trench and putting it in a duct, that might be alright if its a new build and there was a digger there, would want to dig down at least 500mm with massive conifers where the run is, no thanks. Surface in a situation I think is the better bet and safer bet, where I have to cross the ground from the fence to garage will dig it down and run it in duct. Allowing for full demand in the garage at 8kw, will never reach that but never know in the future if it was made into a workshop. Yes will put it on a 50A MCB in the house, which will go to a 2 way rcd board in the garage.
 
  • Like
Reactions: DPG
Seems like the trench method is not really practical. In the circumstances I can't see a major issue running it along the concrete fence. Might not be ideal but not really going to cause any problems. At least it's visible.

What's the 8kw loading likely to be? Seems high.
 
Just allowing for full demand on the ring and lighting circuit, later down the line may wish to add car charging point, heater in garage etc. Also want a decent size on the earth back to MET.
 
Good sparks can be hard enough to source...but a competent witch,once found,should be treasured.

Hats are good for splaying cores,working live...just throwing it out there...
i once found a competent witch. married her. she was a good cook, but my god, she could nag for England.
 
  • Funny
Reactions: PEG and DPG
i once found a competent witch. married her. she was a good cook, but my god, she could nag for England.
Mine has a City and Guilds in Nagging. Not a Electrical Trainee course either many years of training, followed by many years of honing the nagging equivalent of an Oscar, like a fine wine it matures as the years pass.
 
Last edited:

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Garage supply using PME or earth rod.
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
30

Advert

Thread statistics

Created
cairns1990,
Last reply from
Pete999,
Replies
30
Views
15,643

Advert