Got called to a property where the home owner said they got a belt off the shower head and also a big tingle off a tap.
Quickly found 240 on the pipework, strait to fuseboard and pull the main isolator.
Re-check, and still 240 on the MET!
TNS system, so carefully remove the supply earth from the MET
House now dead, 240 on the suppliers earth!
Tell owner there is a problem with the supply cable and I need to call energy distributor.
Owner now sheepishly admits to hitting a 'old bit of wire' in the garden a couple of weeks ago.
The problem did not arise until the rains set in.
I think he did well to put 240 on his earth but not blow the main substation fuse.