Well I stand to be corrected as I dont have a full manual (the quick guide doesn't mention it) but I have never had trouble testing type B RCDs.
How would the type affect the earth leakage trip though?
OK thanks for that.. I'm getting confused with the type B fuse curve, as in a type B rcbo.It's not an earth leakage trip, it's a residual current trip.
The type denotes the various types of residual current that the RCD will operate with. type B RCDs are designed to cope with residual currents with a DC component, and will need testing differently to a type AC RCD. Whilst it will trip on a normal RCD test you will not be testing it properly.
The fact that a type B RCD is designed to ignore DC currents might explain why it trips on an non-trip loop test since testers use DC to saturate the coil of a normal RCD to prevent it tripping.
Reply to Help!!!! Metrel Mi3000 tester problem in the Electrical Tools and Products area at ElectriciansForums.net
Thanks for visiting ElectriciansForums.net, we hope you find the Electricians Tools you're looking for. It's free to sign up to and post a question yourself to find a tool or tool supplier either local to you, or online. Our community of electricians and electrical engineers will do their best to find the best tool supplier for you.
We also have a Tiling Tools advice from the worlds largest Tiling community. And then the Plumbers Forums with Plumbers Tools Advice.
We get it, advertisements are annoying!
Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.